The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
09/27/16 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 13
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 49 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#205702 - 03/22/12 10:23 PM 20 Amp Split
JimOVWA Offline
New Member

Registered: 03/22/12
Posts: 3
Loc: CANADA
Hi all,

Why is it new homes do not have 20 amp splits in the kitchens? Cost aside (GFCI and wire), wouldn't it be reasonable to install splits? I have a 1500w kettle - 12.5 amp, if I add a griddle at 1500 watts and a toaster and blender???? Blown fuses here all the time. Would it not be more logical, since we are using such high powered items in our kitchens now a days, to up the amps on the kitchen splits? Some kitchens are small so plugs can be limited.

Jim

Top
2014 / 2011 NEC & Related Books and Study Guides
#205706 - 03/23/12 07:24 AM Re: 20 Amp Split [Re: JimOVWA]
jdevlin Offline
Member

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
A 15 amp split will be sufficient for two of those devices. The 20 amp option was added to allow GFCI receptacles to be used near the sink. Otherwise you would need to install 15 amp GFCI breakers to use split circuits near the sink.
If you like you can install 20 amp splits. If you do it near the sink you will need 20 amp double pole GFCI breakers.


Edited by jdevlin (03/23/12 07:25 AM)

Top
#205710 - 03/23/12 09:54 AM Re: 20 Amp Split [Re: JimOVWA]
JimOVWA Offline
New Member

Registered: 03/22/12
Posts: 3
Loc: CANADA
Thanx for the reply jdevlin...I have searched everywhere and cannot find a reference to 20 amp splits. Seems like this should be in Code and the 15 amp split requirement deleted since we now have so many high powered devices on our counter tops. If you have a 1500w griddle and 1500w coffee maker on a 15 amp breaker your pushing 25 amps....

Top
#205719 - 03/23/12 02:37 PM Re: 20 Amp Split [Re: JimOVWA]
jdevlin Offline
Member

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
A 15 amp split is minimum. It appears you don't understand how 15 amp split works. There is 15 amps available from each receptacle of the split duplex. That means you can plug in 1500watt griddle AND the 1500 watt coffee maker at the same time.

Top
#205720 - 03/23/12 03:28 PM Re: 20 Amp Split [Re: JimOVWA]
JimOVWA Offline
New Member

Registered: 03/22/12
Posts: 3
Loc: CANADA
Hey jdevlin,

You are right...( If you have a 1500w griddle and 1500w coffee maker on a 15 amp breaker your pushing 25 amps....)...my bad...sorry...

I understand how a 15 amp split works...I don't know what I was drinking when I wrote that....its just that a 1500 w griddle exceeds 80% of the 15 amp circuit (12.5 amps)....and a non split 20 amp circuit with 2 outlets (kitchen) and 2 - 1500w appliances would get you 25 amps on a 20 amp circuit... That's why I asked about 20 amp splits.

Top
#205722 - 03/23/12 04:39 PM Re: 20 Amp Split [Re: JimOVWA]
jdevlin Offline
Member

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
The 80% rule only applies when the load is continuous. People refer to that 80% thing way too often when it does not apply.

Top
#205723 - 03/23/12 06:00 PM Re: 20 Amp Split [Re: JimOVWA]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
A nice upgrade is to provide each receptacle with its own 20 amp circuit. It takes the same space in the panel as a split 15 amp circuit and can be gfi protected at the receptacle.

Top
#205726 - 03/25/12 01:35 AM Re: 20 Amp Split [Re: JimOVWA]
pdh Offline
Member

Registered: 01/20/05
Posts: 354
What I had planned to do in my new home build is use a duplex 5-15 (at least 2 such circuits, if not a separate circuit for each duplex) on a 20 amp circuit, but also include a single 5-20 next to it. The idea is to have at least 2 circuits that 20 amp appliances cannot use (so the capacity is available for multiple smaller appliances). OTOH, a separate circuit for every outlet would eliminate the complication and you can plug a 20 amp appliance anywhere without worry that plugging a 5 amp appliance somewhere else will cause an overload on a circuit.

Top
#205727 - 03/25/12 01:37 AM Re: 20 Amp Split [Re: jdevlin]
pdh Offline
Member

Registered: 01/20/05
Posts: 354
Originally Posted By: jdevlin
The 80% rule only applies when the load is continuous. People refer to that 80% thing way too often when it does not apply.

Maybe he griddles continuously all day long grin

Top