#205675 - 03/21/12 10:21 AM Conduit fill
Willie Offline
New Member
Registered: 03/20/12
Posts: 7
Loc: BC Canada
In a 200 amp residential application can I put 3 conductors of 4/0 and 1 conductor of # 6 into a 2 inch EMT. I am using RW90/X link Aluminum.
Top
Tools for Electricians:
#205678 - 03/21/12 02:28 PM Re: Conduit fill [Re: Willie]
dougwells Offline


Member
Registered: 05/03/03
Posts: 1137
Loc: kamloops BC Canada
Why the #6 ? it this the lateral between the Meter Socket/base and the main disconnect for the Service Panel ??
Top
#205680 - 03/21/12 05:37 PM Re: Conduit fill [Re: dougwells]
Willie Offline
New Member
Registered: 03/20/12
Posts: 7
Loc: BC Canada
Yes, it's a five run with an LB and 4 weather tight connectors between the meter socket & the disconnect switch. I am thinking the # 6 may be a requirement of the CEC although the ground rods should be connected to the disconnect switch I think.
Top
#205682 - 03/21/12 10:22 PM Re: Conduit fill [Re: Willie]
Willie Offline
New Member
Registered: 03/20/12
Posts: 7
Loc: BC Canada
I should add the bare # 6 is to ensure the meter base remains at ground potential even if the LB and related exterior fittings loosen over time. In the meter cabinet there is a ground lug and I am using a ground bushing on the EMT inside the building. BTW, I am using a ground plate, not rods as previously posted.
Top
#205686 - 03/22/12 11:26 AM Re: Conduit fill [Re: Willie]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
The conduit fill is fine but the #6 is not required and will be of little value in a fault. the service pipe gets a bond bushing and the neutral is bonded in the meter base and again at the main switch so adding a #6 only parallels the neutral and the service raceway. I would only add a bond wire if I used PVC as the service raceway even though the neutral meets the minimum code for bonding the meter and mast to the panel. Many inspectors would insist on a bond wire if PVC was used between the meter and panel but it is not required as the grounded service conductor serves both purposes until the neutral bus in the main panel.
Top
#205701 - 03/22/12 10:15 PM Re: Conduit fill [Re: Willie]
Willie Offline
New Member
Registered: 03/20/12
Posts: 7
Loc: BC Canada
mikesh, I appreciate your answer, I always agreed with everyone that the number 6 is NOT a code requirement. My only question was IF it was requested by the local AHJ would I need to upsize the 2 inch conduit as I could not find an actual code reference. The thought of having to change out the conduit (maybe) did not sit well with me. There is a little more to this story but it is no longer relevant as you have answered my question. THANKS to you and dougwells for the feedback. Case closed.
Top
#206183 - 06/01/12 08:11 PM Re: Conduit fill [Re: Willie]
JaredRoch Offline
New Member
Registered: 01/21/12
Posts: 6
Loc: Winnipeg MB
10-814(f) i think says that your EMT will be your bond
Top
#206184 - 06/01/12 08:12 PM Re: Conduit fill [Re: Willie]
JaredRoch Offline
New Member
Registered: 01/21/12
Posts: 6
Loc: Winnipeg MB
and also, if you had to add the number 6 to your conduit, than you would have to follw the steps from Tables 8, 9 and 10 in order to find your conduit size
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals