Locked rotor, no burnout
by andey
Yesterday at 04:48 AM
Temporarily feeding a panel...
by Potseal
09/29/16 11:05 PM
Massive power outage South Australia
by Meadow
09/29/16 06:46 AM
short circuit??
by Meadow
09/29/16 06:43 AM
Norwegian power?
by Meadow
09/29/16 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 12
sparky 10
gfretwell 8
Potseal 7
sparky66wv 6
Who's Online
0 registered (), 281 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#205629 - 03/14/12 10:07 PM 100 W HPS fixture issue
Merlin Offline
Member

Registered: 01/27/04
Posts: 170
Loc: NW Indiana
I have a customer with a 100W HPS fixture on an outbuilding. The fixture is photoeye controlled. Almost everytime that a large load starts in the house (A/C, sewage ejector pump, ect.), the light shuts off and eventually comes back on.

The outbuilding and house are both on seperate loadcenters and feed from the same main panel at the meter. It appears to me that this is caused by voltage drop. Correct?? I even switch the fixture circuit to the opposite phase and it still does it. Could this be simply a photoeye problem, or utility service voltage drop???? Any suggestions?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#205630 - 03/15/12 01:02 AM Re: 100 W HPS fixture issue [Re: Merlin]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
Possibly the transformer is over loaded by other services. What's the incoming voltage at night? It tends to be a little lower in the evenings then the day
_________________________
"Live Awesome!" - Kevin Carosa

Top
#205632 - 03/15/12 06:34 AM Re: 100 W HPS fixture issue [Re: sparkyinak]
wire_twister Offline
Member

Registered: 07/25/07
Posts: 265
Loc: Georgia USA
+1 with sparky, check the voltage in the evening, and look at the size of the transformer, and its load. Call the POCO and ask for someone to come out and look.
_________________________
Jimmy

Life is tough, Life is tougher when you are stupid

Top
#205633 - 03/15/12 06:58 AM Re: 100 W HPS fixture issue [Re: Merlin]
Merlin Offline
Member

Registered: 01/27/04
Posts: 170
Loc: NW Indiana
This is in a rural area, only service on this transformer. voltage. Under start-up surge from A/C or sewage pump, I saw it drop to 112 for about 1/2 second. I switched the fixture to the "higher" phase (121) and it still dropped out under surge.

Top
#205634 - 03/15/12 07:33 AM Re: 100 W HPS fixture issue [Re: Merlin]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6786
Loc: Brick, NJ USA
Merlin:
Did you ck the voltage at the fixture, or the source panel?

Sure sounds like a Vd issue...at the fixture.
_________________________
John

Top
#205635 - 03/15/12 07:37 AM Re: 100 W HPS fixture issue [Re: Merlin]
jdevlin Offline
Member

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
One side higher than the other would indicate possible loose neutral issue.

Top
#205636 - 03/15/12 09:21 AM Re: 100 W HPS fixture issue [Re: Merlin]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
It's probably voltage drop, but try a new bulb to eliminate that before you spend a lot of money on it.

Top
#205637 - 03/15/12 09:51 AM Re: 100 W HPS fixture issue [Re: jdevlin]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
Originally Posted By: jdevlin
One side higher than the other would indicate possible loose neutral issue.


I agree with jdelvin that it could be a loose neutral. When A heavy load start on this service, does any lights on the premises get brighter?
_________________________
"Live Awesome!" - Kevin Carosa

Top
#205639 - 03/15/12 05:24 PM Re: 100 W HPS fixture issue [Re: Merlin]
wire_twister Offline
Member

Registered: 07/25/07
Posts: 265
Loc: Georgia USA
I agree with the possible loose neutral situation also. As far as the transformer, My house is the only load on a 15 KVA pole pig, it is about 60 feet from the pole to my meter, every time my 4.5 ton AC compressor starts there is a noticible flicker in the lights. Put this same load on a 10 KVA pot and it could pull down enough to turn the light out. What kind of meter did you use to measure the voltage when AC started? Most DVOMs are not fast enough to catch the dip, so it is likely the reading you got was on its way back up before your meter settled down. Just my 2 cents.
_________________________
Jimmy

Life is tough, Life is tougher when you are stupid

Top
#205640 - 03/15/12 07:32 PM Re: 100 W HPS fixture issue [Re: Merlin]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Rewire your High Pressure Sodium fixture across 230 VAC instead of 120 VAC.

I'm presuming it has a CWA ( Constant Wattage Autoformer ) with multiple taps.

I also suspect that the wire gauge used to feed it needs 240 VAC.

You've made no mention of the distance to the outbuilding.

Check if the photo-eye can be replaced with a 230 VAC sensor, too.

Every time its voltage pulls low it changes its logical state -- which is the primary cause for the HPS to cut out.
_________________________
Tesla

Top
Page 1 of 3 1 2 3 >