The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 262 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#205574 - 03/10/12 06:09 PM how to properly terminate larger wires in panels
Sparky77 Offline
Member

Registered: 11/15/08
Posts: 13
Loc: Alberta
Anyone have some suggestions on how to properly terminate larger wires in panels? I'm faced with a 200A panel but we are sub feeding a seperate 100A panel on the second floor of the house. 3C #2 AL NMD cable is what we used. The problem now is that the neutral busbar has all the same size holes to terminate and they are all only good for up to #4. The panel is an Eaton Cuttler Hammer.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#205576 - 03/10/12 06:59 PM Re: how to properly terminate larger wires in panels [Re: Sparky77]
sparkyinak Online   content
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
Granted, Canadian code may have something to say on it. Most neutral busses allow a lug kit to be installed to allow a bigger wire to be terminated on them
_________________________
"Live Awesome!" - Kevin Carosa

Top
#205586 - 03/10/12 11:10 PM Re: how to properly terminate larger wires in panels [Re: Sparky77]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Yup, what he said. They make a big lug with a couple of legs that grab 2 slots. Look in the accessory catalog for your panel.
_________________________
Greg Fretwell

Top
#205588 - 03/10/12 11:16 PM Re: how to properly terminate larger wires in panels [Re: Sparky77]
mikethebull Offline
Member

Registered: 03/18/07
Posts: 101
Loc: Rhode Island
I agree with sparkyinak use a lug kit for that panel so long as the panel is rated for a subpanel.