The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Members: Non-Members: Did you know?
by Admin
Today at 02:34 PM
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 36
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Admin), 83 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#205568 - 03/09/12 01:18 PM mca and mocp nameplate
Bravo Offline
Member
Registered: 05/04/10
Posts: 30
Loc: NY, USA
Hi have a chiller rated 208V, 3P, MCA: 46.1, MOPD: 80, RLA: 30. Its been awhile for sizing motor branch ckts but any idea how to size the ckt. & OCPD?

Correct me if I am wrong but last I remember based on the nameplate info conductors can be #6 with 60A circuit breaker?
MCA = minimum current ampacity
OCPD = maximum over current protection device

Where in the NEC doesnt reference sizing ckts per nameplate?

thanks in advance
Top
2017 / 2014 NEC & Related Books and Study Guides
#205569 - 03/09/12 01:43 PM Re: mca and mocp nameplate [Re: Bravo]
electure Offline


Member
Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
NEC Article 440 is the one you want to read for this.

You can use #8 for a MCA of 46.1, with up to an 80 amp hacr breaker or fuses for the MOPD.
Top
#205570 - 03/09/12 01:49 PM Re: mca and mocp nameplate [Re: electure]
Bravo Offline
Member
Registered: 05/04/10
Posts: 30
Loc: NY, USA
#8 is good for 40A in the 60deg C column of table 310.16. I think I need to use this for equipment rated 100A or less?
Top
#205571 - 03/09/12 07:53 PM Re: mca and mocp nameplate [Re: Bravo]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Make sure the terminals in the Chiller are rated for 75 C if you plan on using #8 copper wire. Most equipment of this nature are only rated for 60 C and that would call for a #6. As for the line side of the disconnect (assume it is separate from the Chiller) it probably would be rated 75 and #8 would be fine. The 80a. overcurrent device is proper in either case.
_________________________
George Little
Top