The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
sparky 4
Who's Online
0 registered (), 265 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#205512 - 02/28/12 07:36 AM dry type transformer failure
Danny00915 Offline
New Member

Registered: 02/23/12
Posts: 1
Loc: Singapore
I have a 50kVA dry type transformer which had failed, with rating:

1. Input (LV, primary winding): 400V, 72.17A
2. Output (HV, secondary winding): 21.5kV, 1.34A

The failed area was found to be the HV winding, where short circuit of winding and sign of local overheating was observed . Calculations showed no overload to input or output.

What would have cause the overheating? probable cause of the failure?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#205526 - 02/29/12 12:18 PM Re: dry type transformer failure [Re: Danny00915]
geoff in UK Offline

Registered: 12/30/02
Posts: 171
Loc: UK
Simple transformer insulation failure? It only takes one turn to short out and rapid overheating follows causing progressively more insulation failure.
Possible causes? Weak insulation since manufacture, moisture ingress, vibration, transient voltage surge, hotter than designed operating environment, - I'm sure there are more I can't just think of.

#205527 - 02/29/12 02:30 PM Re: dry type transformer failure [Re: Danny00915]
gfretwell Offline


Registered: 07/20/04
Posts: 9023
Loc: Estero,Fl,usa
Is it getting plenty of air? These things, in confined space, can heat up quickly.
Greg Fretwell

#205528 - 02/29/12 07:22 PM Re: dry type transformer failure [Re: Danny00915]
HotLine1 Offline


Registered: 04/03/02
Posts: 6791
Loc: Brick, NJ USA
100% agree with that Greg> I remember a plant where some employees used a 75KVA for a lunch warmer with help from some cardboard & welding screen curtains! A situation that could have become a njghtmare.

#205555 - 03/03/12 02:31 PM Re: dry type transformer failure [Re: Danny00915]
Lostazhell Offline

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
We had an old Westinghouse padmount 12kv pri 480V sec 1000kva that inadvertently was loaded up with >1600 hp in oil pumping units & steam genset pumps & blowers.. It ran this way for quite some time & wasn't discovered until we ran into some low voltage issues in a control room... The load was divided up with 2 banks of 167s added. The padmount still runs part of the field..