The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (gfretwell), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#205432 - 02/20/12 08:12 PM Bonding Ductwork??
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Scenario: Sheetmetal ductwork for a dust collector system in a woodshop.

(5 HP, 3 phase, 208 volt motor)

Does the ductwork require any bonding? How about static?

Any code references appreciated.
_________________________
John

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#205436 - 02/20/12 10:33 PM Re: Bonding Ductwork?? [Re: HotLine1]
gfretwell Online   content

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I would assume the duct work gets bonded via the EGC to the dust collector motor and enclosure. This is similar to a duct heater.
Static is a whole 'nother thing, particularly if this is a plastic duct. In some of the woodworking BBs they have discussions about this. The fear is "lightning" in the duct could cause an explosion. I would think simply bonding a metal duct would bleed off the static charge.

I do not know of any article that deals with this unless you can call it "pipe" 250.104(B)
_________________________
Greg Fretwell

Top
#205437 - 02/21/12 07:15 AM Re: Bonding Ductwork?? [Re: HotLine1]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Greg:
I'm looking for any requirement, other than 'spec' for this.

The two woodshops I installed dust collector systems in years back both had duct bonding on the 'specs'.
_________________________
John

Top
#205439 - 02/21/12 08:24 AM Re: Bonding Ductwork?? [Re: HotLine1]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I believe the bonding requirements are in the Mechanical code, and are dependent on the CFM of the unit. That is, your typical home workshop collector isn't big enough to require it.

Ironically, the problem is with plastic ducts, rather than metal ones.

Top
#205440 - 02/21/12 11:39 AM Re: Bonding Ductwork?? [Re: HotLine1]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Reno:
Thanks for the input. I searched the mech code to no avail, it sends ya to NFPA codes, and that is vague also.

I dumped this back to the design pro to see what kind of response I get from him/them.
_________________________
John

Top
#205441 - 02/21/12 12:06 PM Re: Bonding Ductwork?? [Re: HotLine1]
gfretwell Online   content

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Maybe this gets back doored in by the manufacturer's installation instructions.

Other than that I can't find anything either.

It is probably like steel studs and the NFPA is waiting for a body or two.
_________________________
Greg Fretwell

Top
#205600 - 03/12/12 06:52 AM Re: Bonding Ductwork?? [Re: HotLine1]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
John,

I had computer issues the past month so I wasn't on line.

I have seen the plastic dust collectors have a bonding wire run along side of them to discharge the static when sucking up the dust, but I haven't seen too many metal duct collector systems. My guess is that the metal will bleed off any static as it starts to build up as long as the metal duct is attached to a grounded piece of equipment.

Top
#205601 - 03/12/12 11:55 AM Re: Bonding Ductwork?? [Re: HotLine1]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Harold:
Thanks for that. At the moment, the job seems to be in limbo for some reason.
_________________________
John

Top
#205602 - 03/12/12 12:14 PM Re: Bonding Ductwork?? [Re: harold endean]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
From what I can find on the subject, the general consensus seems to be that with that type of installation the bare wire should be run inside the plastic duct to actually be effective. Placing it outside supposedly does nothing to dissipate any static build up inside the duct, which apparently is where the dust ignition problems occur.

Top
#205603 - 03/12/12 12:18 PM Re: Bonding Ductwork?? [Re: HotLine1]
gfretwell Online   content

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
They do make this stuff (conductive duct) but it ain't cheap.

http://www.globalindustrial.com/p/hvac/f...5-ft-long-strap
_________________________
Greg Fretwell

Top