The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by LongRunner
Today at 07:42 AM
100% breakers?
by Texas_Ranger
Today at 06:13 AM
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
gfretwell 11
sparkyinak 10
ghost307 10
Trumpy 8
Who's Online
0 registered (), 266 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#204952 - 01/24/12 08:59 AM 517.13 (A)Care Facility Grounding
wewire2 Offline
Member

Registered: 11/14/02
Posts: 246
Loc: California
The commentary after 517.13(A)
reads "the second component in this approach is the separate insulated grounding conductor required by 517.13 (B. therefore, the metal raceway or metal cable or sheath must qualify as an equipment grounding conductor in accordance with 250.118, INDEPENDENT of any separate wire-type equipment grounding conductor."
Shouldn't it read "in addition to?" The way it reads seems to require the insulated conductor to be isolated back to the the panel and not bonded in the box as a parallel grounding method.

Top
2014 / 2011 NEC & Related Books and Study Guides
#204956 - 01/24/12 06:22 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6824
Loc: Brick, NJ USA
Point made & taken. Perhaps a 'bad' use of the word 'independent'.

Logic, is an insulated EGC and an approved metalic wiring method.
_________________________
John

Top
#204969 - 01/25/12 07:24 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
wewire2 Offline
Member

Registered: 11/14/02
Posts: 246
Loc: California
Thanks for the affirmation John.

Top
#204970 - 01/25/12 07:56 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6824
Loc: Brick, NJ USA
It would be interesting to see if we get any other responses. Maybe George? Greg?
_________________________
John

Top
#204971 - 01/25/12 08:29 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Doesn't 250.48 Cover that??Since its not referred to as an
isolated ground as in 250.146(D)
Yoopersup

Top
#204972 - 01/25/12 08:30 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Should be 250.148 Not 250.48 Opps

Top
#204977 - 01/25/12 11:02 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
wewire2 Offline
Member

Registered: 11/14/02
Posts: 246
Loc: California
Thanks Yoop
Yes,It's standard procedure to crimp the grounds together and land them in the box that contains a non I.G. device or a splice. In using the dictionary definition below, the wording in the NEC commentary is correct. Both systems can still be referred to as functionally independent even though they are connected. I now know that independent does not necessarily mean separate. Live and learn huh!!


Independent: Not dependent on anything else for function, validity, etc.; separate two independent units make up this sofa