#204952 - 01/24/12 08:59 AM 517.13 (A)Care Facility Grounding
wewire2 Offline
Member
Registered: 11/14/02
Posts: 244
Loc: California
The commentary after 517.13(A)
reads "the second component in this approach is the separate insulated grounding conductor required by 517.13 (B. therefore, the metal raceway or metal cable or sheath must qualify as an equipment grounding conductor in accordance with 250.118, INDEPENDENT of any separate wire-type equipment grounding conductor."
Shouldn't it read "in addition to?" The way it reads seems to require the insulated conductor to be isolated back to the the panel and not bonded in the box as a parallel grounding method.
Top
2017 / 2014 NEC & Related Books and Study Guides
#204956 - 01/24/12 06:22 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Point made & taken. Perhaps a 'bad' use of the word 'independent'.

Logic, is an insulated EGC and an approved metalic wiring method.

_________________________
John
Top
#204969 - 01/25/12 07:24 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
wewire2 Offline
Member
Registered: 11/14/02
Posts: 244
Loc: California
Thanks for the affirmation John.
Top
#204970 - 01/25/12 07:56 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
It would be interesting to see if we get any other responses. Maybe George? Greg?
_________________________
John
Top
#204971 - 01/25/12 08:29 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Doesn't 250.48 Cover that??Since its not referred to as an
isolated ground as in 250.146(D)
Yoopersup
Top
#204972 - 01/25/12 08:30 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Should be 250.148 Not 250.48 Opps
Top
#204977 - 01/25/12 11:02 PM Re: 517.13 (A)Care Facility Grounding [Re: wewire2]
wewire2 Offline
Member
Registered: 11/14/02
Posts: 244
Loc: California
Thanks Yoop
Yes,It's standard procedure to crimp the grounds together and land them in the box that contains a non I.G. device or a splice. In using the dictionary definition below, the wording in the NEC commentary is correct. Both systems can still be referred to as functionally independent even though they are connected. I now know that independent does not necessarily mean separate. Live and learn huh!!


Independent: Not dependent on anything else for function, validity, etc.; separate two independent units make up this sofa
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 84 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals