The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
Yesterday at 09:33 AM
breaker meltdown
by crselectric
Yesterday at 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 17
sparky 9
gfretwell 9
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 237 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#204912 - 01/21/12 07:12 AM sizing of Transformer
volt Offline
New Member

Registered: 09/23/09
Posts: 1
Loc: canada
hi , i have a generator that gives me 600v 3ph 120 amps and would like to have 120/208 3ph .
What size of Transformer should i use

Thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#204917 - 01/21/12 09:34 AM Re: sizing of Transformer [Re: volt]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
600 volts x 120 amps x 1.73 = 124,560 volt amps

Standard transformer sizes are 112 1/2 kva (smaller) or 150 kva (larger)