The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 106 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#204740 - 01/04/12 11:45 AM temporary roll up generator
Bravo Offline
Member

Registered: 05/04/10
Posts: 30
Loc: NY, USA
I have to replace an existing unit substation that supports a 50,000 sf building. During construction, I am proposing a temporary roll up generator with a termination cabinet between the generator and existing dist. equipment to provide temporary electrical services during construction. The generator will feed a 800A MCB dist. panel. I understand per Art 590 (2011) a temporary service must be installed as a permanent installation er Art 230.

Are there any concerns that I should be aware of? I feel like I am missing something?

Thanks in advance.

Top
2014 / 2011 NEC & Related Books and Study Guides
#204742 - 01/04/12 12:00 PM Re: temporary roll up generator [Re: Bravo]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
dbravo:

IMHO, you should refer to 590.2 (b), check with the local AHJ regarding your proposed temp install.

Conforming with 230 part 1 thru 7 requirements, should not pose any issues, based on what you described above.

MOCP at the gen, feeder to your MDP and branch circuits feeding your loads.