#204486 - 12/14/11 09:21 AM Filling out a load sheet
Wak Offline
New Member
Registered: 12/14/11
Posts: 1
Loc: New Jersey
PSE&G wants me to fill out a load sheet for my electric service, even though there is existing service. They say since electric was off for over a year I have to fill out a load sheet...The property has three meters ( it is a two family). What do I look for as far as watts, amp, phase, existing load in Kw etc...
Top
Work Gear for Electricians and the Trades
#204487 - 12/14/11 11:21 AM Re: Filling out a load sheet [Re: Wak]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Wak:

Welcome to ECN Forums from one of the 'Jersey Guys'

As to your inquiry, the ESI for PS is a usual request. Basically, a 2 family with a 'house' panel you would take the 'calc loads for each apt, and the common areas and submit a total in KW.

Use the NEC load calcs within the '08 NEC for basic guides.

Have you spoke to the PSE&G wiring inspector? You do not have any 'area' of NJ in your profile.



_________________________
John
Top
#204488 - 12/14/11 11:24 AM Re: Filling out a load sheet [Re: Wak]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
I moved this to the general Discussion Area
_________________________
John
Top
#204499 - 12/14/11 11:20 PM Re: Filling out a load sheet [Re: Wak]
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
John,
Thanks for moving this topic! thumbs thanks

WAK;

As John has mentioned, contact the Utility Company and verify the request with a Service Planner.

Seems to me the POCO is requesting Load Calculations for this Existing Service, so as to verify the Existing Service Feeders (and maybe the Transformer too) will handle the peak Calculated Loads.
They (POCO) may think there has been some Remodeling done on the Property, which could affect the Peak Load; which is likely to occur in One Years' time.

An accurately compiled Load Calculation Database will include the Calculated Loads for both Tenants and the "House Panel".
NEC Article 220 contains the information.
Basically, the Loads will include:

a: 3 VA / Square Foot - General Lighting,
b: 1500 VA per Small Appliance Circuit,
c: Electric Cooking Appliances,
d: HVAC,
e: Electric Water Heating,
f: Laundry Equipment,
g: Electric Motors.

Wish there was more to include, but I rarely perform Residential Load Calculations!

Good luck!

-- Scott
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#204502 - 12/15/11 06:29 AM Re: Filling out a load sheet [Re: Wak]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Scott:

thanks for some additional details!!
_________________________
John
Top
#204511 - 12/15/11 01:23 PM Re: Filling out a load sheet [Re: Wak]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
This is a sample I found of a multifamily load calc that is based on the '08 NEC. It may or may not help, but it looks like it could give you the general gist of things to include along with some other stuff like the minimum neutral size, fault current and voltage drop calcs.

Multifamily Load calc
Top
#204514 - 12/15/11 05:56 PM Re: Filling out a load sheet [Re: Wak]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Kjay:

Thanks for that!!

Scott may want to consider putting that is the Tech Section.

_________________________
John
Top
#204524 - 12/17/11 08:19 PM Re: Filling out a load sheet [Re: Wak]
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Quote:

Scott may want to consider putting that is the Tech Section.


Great suggestion!

New Post has been made at the Technical Reference area for this item under the topic:

Load Calculations Example-Multi Family Dwelling

*** Note: Clicking on the Link above will open that page in a new Window. ***

-- Scott
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#204525 - 12/18/11 10:31 AM Re: Filling out a load sheet [Re: Wak]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Scott..
Thanks for that!
Useful guide IMHO
_________________________
John
Top
#204612 - 12/24/11 08:37 PM Re: Filling out a load sheet [Re: Wak]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
Wak,


Welcome to the board from another Jersey guy. Though I am here less than I would like to be. When I worked in PS territory, we always had to fill out a PSI or a preliminary service inspection in order to get a meter pan and turn the service on. Though it has been a dozen or so years that I was out in the field. JCP&L also wants a typical layout when they go to hook up a new service for the first time. They will give you a "DR" number or "R" #. You give that to the AHJ when he sends in your cut-in card.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 84 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals