The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 9
sparky66wv 8
Vlado 6
Who's Online
1 registered (zapped208), 256 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#204272 - 11/25/11 11:03 AM Automating Manual Gen Transfer Swtich...
johnmixdecn Offline
New Member

Registered: 11/25/11
Posts: 1
Loc: NY
Hi all. I have a setup with a diesel genset. This genset feeds a 3 phase panel (120/120/120). This panel has 4 double breakers, each feed a single phase panel, each of which has a manual transfer switch that switchs the panel between line power and the 3 phase gen panel. This has worked well for years.

What im looking to do is to automate this. Installing 3 auto transfer switchs is beyond my budget.

What im thinking is I will write a program that runs on a dedicated PC (on battery backup of course) that will watch the incoming power, and when we lose power, or a even lose a single phase...it will start and warm up the genset. Then it will wait a few minutes then flip each transfer switch over. I have writen a similar program for a smaller application that was in a communications shed in the woods. It worked great.

This is where my question comes in. Would it violate code in any way to have an electric actuator push/pull the handle of the transfer switchs from "Line" to "Gen"? I cant see how it would since this is external from any electrics and is doing this same thing as a human fliping the switch.

--John

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#204273 - 11/25/11 12:20 PM Re: Automating Manual Gen Transfer Swtich... [Re: johnmixdecn]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
When you change a manual transfer switch to automatic (any way you do it) you do bring in the requirement that the generator now must be capable of maintaining the entire connected load.
Does your program do load management?
Other than that you might bump into 110.3(B) about using equipment the way the manufacturer's instructions specify.
_________________________
Greg Fretwell