The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Yesterday at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 224 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#204260 - 11/22/11 07:17 PM Tapping parrellel conductors
sudsy4 Offline
Member

Registered: 04/24/02
Posts: 32
Loc: Elizabeth,PA USA
Any suggestions on how to tap 4 panels (350MCM each) from 3 parrallel 600MCM feeders in a gutter?
_________________________
Bill

Top
#204263 - 11/22/11 09:15 PM Re: Tapping parrellel conductors [Re: sudsy4]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
'Polaris' type terminations; 600 to 350 range, 7 barrel, or 8 to be safe.
_________________________
John

Top
#204264 - 11/23/11 06:00 AM Re: Tapping parrellel conductors [Re: sudsy4]
wire_twister Offline
Member

Registered: 07/25/07
Posts: 265
Loc: Georgia USA
I am with John on this one. polaris connectors are the way to go, hope it is a BIG gutter!
_________________________
Jimmy

Life is tough, Life is tougher when you are stupid

Top
#204267 - 11/23/11 06:02 PM Re: Tapping parrellel conductors [Re: sudsy4]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6805
Loc: Brick, NJ USA
sudsy4:

The 8 barrel Polaris is <11" long, with cable entry from either side. So, you need a troff at least 12".

They make a 'stacker' model also, but...it's not UL Listed.

Check out the link below.

http://www.polarisconnectors.com/pdfs/NSi/IPLD_series.pdf
_________________________
John

Top