Can the low-volt wiring to a generator annunciator panel pass through the same junction box (without a partition) containing low-volt wiring corresponding to medical gas valves, gauges, and controls in a hospital?
Top
2017 / 2014 NEC & Related Books and Study Guides
#204136 - 11/15/11 04:48 PM Re: mixing of systems? [Re: triple]
sabrown Offline
Member
Registered: 12/12/02
Posts: 302
Loc: Ogden, Utah, USA
I do not know, but I would ask myself this as a quick test to say no. Is the system that I plan on mixing with a critical system. If it were I would not ask any further. My opinion here is not worth anything, but I noticed you were on rright now and that no one had responded.
Top
#204137 - 11/15/11 05:52 PM Re: mixing of systems? [Re: triple]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
I have to agree with sabrown. I can't put a specific article on it. It's best to stay away from the critical system.
_________________________
John
Top
#204139 - 11/15/11 07:16 PM Re: mixing of systems? [Re: triple]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Is this a 517.30(C)(1) thing? What is the generator doing?
_________________________
Greg Fretwell
Top
#204140 - 11/15/11 08:42 PM Re: mixing of systems? [Re: triple]
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Greg:
IMHO, to provide an answer of allowed or not, a lot more details would have to be provided by the OP. He mentioned 'critical system', gas valves, control and no specific area for the 'j' box. I'm curious if he has any plans/specs. for the install.

_________________________
John
Top
#204161 - 11/17/11 11:15 AM Re: mixing of systems? [Re: triple]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
I don't know if Ann. wires come into this but read .
700.9 (B) p. 1108 2008 handbook & (D)3 page 1112 2008 nec code handbook.

Yoopersup
Top
#204186 - 11/18/11 07:06 PM Re: mixing of systems? [Re: triple]
triple Offline
Member
Registered: 04/01/02
Posts: 184
Loc: Wisconsin
Medical gases are oxygen, nitrogen oxide, and oxygen. They are piped to many rooms in a hospital. Gauges read their pressures and go into alarm when not within spec. I never mentioned "critical systems" but of coarse the most important purpose of the generator in a hospital is to provide critical and emergency power when called upon to do so. Generator annunciator wiring is not circuit wiring. Both the med-gas and generator wires I am describing are for status indicating only. The conductors feeding the gas valves I mentioned before are actually fed separately.
Top
#204193 - 11/19/11 01:11 AM Re: mixing of systems? [Re: triple]
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
On the face of it,
I would say no.
Make life easier for yourself and just run a seperate conduit.
At least then there will be no question of your stuff mucking up anything that has been pre-installed.
Even though we are talking about low-level signalling stuff here, its best to have some sort of segregation, even if for fault-finding purposes down the track.
By that I mean, who hasn't opened up a but of wire troughing and found a tonne of wires all the same colour?

Also with new conduit, you have the opportunity to identify your work as being say "GEN-ANN" along the way.

Just my thoughts.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 84 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals