#204119 - 11/14/11 09:52 AM Article 511 Required sealing
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
511.9
If a conduit does Not pass thur a Classified
area sealing is Not required.
See page 771 Exhibit 511.1.
If a conduit comes from Outside the building goes up to 28inches then enters a box inside a poured concrete wall it never enters the classified area. Thus Seal not required.
Whatca think??
Same as example on page 771 but conduit comes from outside & stays inside the outer wall.
Yoopers
Top
2017 / 2014 NEC & Related Books and Study Guides
#204121 - 11/14/11 12:09 PM Re: Article 511 Required sealing [Re: Yoopersup]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
IMHO, you are correct, no seal required.
_________________________
John
Top
#204189 - 11/18/11 08:10 PM Re: Article 511 Required sealing [Re: Yoopersup]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Done???
_________________________
John
Top
#204201 - 11/19/11 11:01 AM Re: Article 511 Required sealing [Re: Yoopersup]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
It sounded pretty done to me but you probably still need some duct seal to prevent the cold air, condensation thing. That is not a real seal off tho.
_________________________
Greg Fretwell
Top
#204208 - 11/20/11 12:55 PM Re: Article 511 Required sealing [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Thanks guys it just what I figured ,
Top
#204226 - 11/21/11 03:11 PM Re: Article 511 Required sealing [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Just got written up by Local Inspector for doing it.
Guess 90.4 comes into play!
Yoopersup
Top
#204227 - 11/21/11 03:46 PM Re: Article 511 Required sealing [Re: Yoopersup]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
It all gets down to what is "inside". (which side of the wall is the border).
I can put my "flush mounted jelly jar" hat on and see his point. We call the outside wall the border there and let them use Romex to a dry location octagon box.
He must be saying the conduit is traveling through the classified location, inside the wall.
_________________________
Greg Fretwell
Top
#204230 - 11/21/11 06:37 PM Re: Article 511 Required sealing [Re: Yoopersup]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
I take Yoops job from the OP as the box and conduit being encased in a poured concrete wall. I can't see how that can be 'in' the classified area, also with the dimensions he posted.

On that thought, unprotected service conductors encased in 2" of concrete are 'outside the structure'. Although Yoop did not provide wall thickness dimensions, or a conduit size. it sounds like it could be 2"+ encased in poured concrete.

_________________________
John
Top
#204235 - 11/22/11 06:52 AM Re: Article 511 Required sealing [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Right he says even thought its in 2 inches Concrete coming from outside its in classified area. I disagree. \
Conduit comes below ground up Outside poured wall to Panel.
I know this area was revised in 2005 but I didn;t find that deleted??
Yoopersup
Top
#204241 - 11/22/11 01:16 PM Re: Article 511 Required sealing [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan



Edited by electure (11/22/11 08:23 PM)
Edit Reason: to add image from Photo Gallery
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (ghost307), 67 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals