#204034 - 11/04/11 09:41 PM running wire on botom of floor joists
homerjones Offline
Member
Registered: 12/08/07
Posts: 35
Loc: 0nt.
anybody know whether or not running wire on the bottom of floor joists in a basement is acceptable, if your going to put up a tbar ceiling. i have a house which only has 2x8 floor joist's and i would like not to drill through them. to the best of my knowledge the answer is no, but maybe somebody know's the codebook better than i do. or know's the inspector will allow it under these circumstances. i'm in ontario by the way
Top
Tools for Electricians:
#204046 - 11/05/11 10:50 AM Re: running wire on botom of floor joists [Re: homerjones]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
12-514(b) says you can if the wire is protected from mechanical injury. Above the ceiling is okay, but isn't okay until the ceiling is installed. The traditional protection is a running board beside the wires or running the wires on the side of the beam.

If you keep the holes in the middle of the joist, it won't weaken the joists. The rule refers to Appendix G that has a cross reference to the National Building Code 9.23.5 about drilling joists. Last time I looked, I couldn't even find a carpenter with a copy of the National Building Code and mine is from 1985. Perhaps someone has a more up-to-date copy. In the meantime, the rule WAS that the hole had to be 50mm from the edge and have a diameter less than 1/4 the depth of the joist.
Top
#204223 - 11/21/11 12:06 PM Re: running wire on botom of floor joists [Re: homerjones]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Don't drill trusses.
_________________________
Greg Fretwell
Top
#204269 - 11/24/11 04:36 PM Re: running wire on botom of floor joists [Re: gfretwell]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Originally Posted By gfretwell
Don't drill trusses.

Without approval by the structural engineer. Greg you can drill some trusses but only in very specific areas, of certain maximum diameter, etc. But drill it in the wrong place and lots of trusses need to be completely replaced.
That said, your advice is still good as getting it wrong or without the engineers approval can be very expensive.
Top
#204270 - 11/24/11 07:18 PM Re: running wire on botom of floor joists [Re: homerjones]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
The typical I-beam truss that I've encountered has factory provided KOs that blow out with a light tap of a hammer.

The worst place to open up a large hole in manufactured trusses is at the ends. That's where the stress is the greatest.

Manufactured beams are another story altogether...

We never penetrate them -- and the factory does not provide any KOs, either.

_________________________
Tesla
Top
#204620 - 12/25/11 01:24 AM Re: running wire on botom of floor joists [Re: homerjones]
homerjones Offline
Member
Registered: 12/08/07
Posts: 35
Loc: 0nt.
this is an old house guys no engineered trusses here. the original floor joists are just 2x6s thats why i dont want to drill at all.
Top
#204659 - 12/27/11 08:34 PM Re: running wire on botom of floor joists [Re: homerjones]
wacked Offline
Member
Registered: 12/19/06
Posts: 33
floor joists or trusses....what is it. Is there not a difference? Never drill a truss as far as i'm concerned.
Top
#204671 - 12/28/11 11:09 PM Re: running wire on botom of floor joists [Re: homerjones]
homerjones Offline
Member
Registered: 12/08/07
Posts: 35
Loc: 0nt.
some of the replys are refering to the engineered trusses made out of chipboard and 2x2s this is an old house with 2x6 floor joists. i'm hoping to not have to drill holes in them if they were 2x 10s as they should have been then no problem.
Top
#204672 - 12/29/11 05:51 AM Re: running wire on botom of floor joists [Re: homerjones]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
Iím in the US so not familiar with the CEC, but in basements and crawl spaces of older buildings with under sized joists we used to shim and screw one or two 1X running boards across to the bottom of the joists and staple the wiring to that. The width of the boards was determined by the number of wires to be run. We would cut them at various angles to go around corners or change direction to follow the room or area. It looked really neat and is allowed to be done this way in the NEC. Hopefully there is enough ceiling height to allow the T-bar ceiling track to mount just below this level.
If there is not enough room to use the running boards, I would ask your inspector if he will allow you to mount the wires directly to the bottom of the joists and protect them with 1X strips on each side. This isnít really ideal as far as the NEC is concerned, but once the T-bar ceiling is up, IMO it shouldnít be much of an issue.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 56 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals