#203852 - 10/28/11 10:34 AM strange motor wiring
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I helped my neighbor replace a motor on his boat lift. Usually these are the typical 6 wire motor on a drum switch. (4 wires to the motor) This one was still the 6 wire motor but there were only 3 wires to the motor. After a lot of head scratching and looking into the controller, this is what I figured out. Does this look normal? It does work.



_________________________
Greg Fretwell
Top
Work Gear for Electricians and the Trades
#203858 - 10/28/11 01:23 PM Re: strange motor wiring [Re: gfretwell]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
It's new to me but I can't see why it wouldn't work.
Top
#203860 - 10/28/11 02:10 PM Re: strange motor wiring [Re: gfretwell]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
I found this boat lift motor diagram that looks like it may similar be what you have.

Lift Motor Wiring
Top
#203861 - 10/28/11 02:19 PM Re: strange motor wiring [Re: gfretwell]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Greg:
I had one for a 'friend' on the bay side of the barrier island. He took it apart, & tried really hard to see how bad he could screw it up. Wound up exactly as your diagram & works well.

_________________________
John
Top
#203865 - 10/28/11 05:53 PM Re: strange motor wiring [Re: KJay]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Originally Posted By KJay
I found this boat lift motor diagram that looks like it may similar be what you have.

Lift Motor Wiring


That is the normal 4 wire thing you see on the Furnas site for a drum switch.

They are doing this with 3 wires. The difference is the start winding is in series with one of the run windings.
I haven't noticed any loss of starting power but it has to be getting less "kick".
_________________________
Greg Fretwell
Top
#203866 - 10/28/11 06:00 PM Re: strange motor wiring [Re: gfretwell]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
John, let me guess, this was a remote control lift?

I drew the controller as a DPDT switch just to show how the logic works. It is really done with a box full of relays. I am still not sure why it is done this way. They still have 2 relays per direction. My guess is the original design was one relay each way but that would have left one side energized. (as my picture is drawn)


Edited by gfretwell (10/28/11 06:02 PM)
Edit Reason: add a thought
_________________________
Greg Fretwell
Top
#203867 - 10/28/11 06:36 PM Re: strange motor wiring [Re: gfretwell]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Greg:
You got it! A strange setup, but it works!

He was an office guy, that likes to think that ECs make to much $$. He changed his outlook when I lifted his week old Pursuit up & down! He was playing with the wiring for two days before the 911 call.

_________________________
John
Top
#203871 - 10/28/11 09:09 PM Re: strange motor wiring [Re: gfretwell]
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Looks good to me.

Windings #1-#2 + #3-#4 are the Split Coil Main (Run) Windings.
The Winding at Terminal #8 is the Auxiliary (Start) Winding, which is in Series with the Start Capacitor and the Start Switch. Start Switch Terminal is #5

Appears to be a Dual Voltage ("Low Volts" = 120V, "High Volts" = 240V) 1 Phase Capacitor Start Induction Motor, setup for "High Volts" (240V) Input.

The Auxiliary "Start" Circuit (Winding, Capacitor & Start Switch) connects to the "Center Tap" point of the Main "Run" Windings. This results in 1/2 the Motor Terminal Voltage across the Start Circuit - or 120V.
Look sort of familiar??? Works the same as the 120/240V 1 Phase 3 Wire Transformer feeding it!

With the Start Circuit connected via the Center Tap, the Capacitor may be rated for 120V, even though the Run Windings may be connected across 120V or 240V.

As to the Connections Scheme, the "Key" to proper connections (per "Forward" and "Reverse"), is to "Make" the Start Winding reduce the Mag. Field Strength on One "Side" of the Run Winding.
This is what determines the Startup Rotation.

Using Greg's Schematic example above, Connecting the Start Circuit Terminal #5 to "L2" will start the Rotor in the Counter-Clockwise Direction (normal "Forward" direction).
The Start Winding reduces the Field on the "Lower" Winding Section (#3-#4), causing the Rotor to "Fall" in that direction.

Connecting the Start Circuit Terminal #8 to "L2" will start the rotor in the Clockwise Direction ("Reverse" direction).
The Start Winding reduces the Field on the "Upper" Winding section (#1-#2), causing the Rotor to seek that direction.

BTW, if this Motor is a PSC (Permanent Split Capacitor) type, no Centrifugal Start Switch will be included in the Auxiliary Circuit, and the Auxiliary Circuit is always connected to the AC Input during Motor Operation.

-- Scott
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#203873 - 10/28/11 09:29 PM Re: strange motor wiring [Re: gfretwell]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
This is what the manufacture has in his instructions so you can see it was hard to make the leap to what they had.

_________________________
Greg Fretwell
Top
#203874 - 10/28/11 10:01 PM Re: strange motor wiring [Re: gfretwell]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
A+ to the guy who figured out the wiring the way you found it. I wonder about the instant reverse switch, though.
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 65 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals