I don't quite understand when/why the neutral needs to get switched when a generator is involved in a residential system. Can you explain please.

i am installing a manual transfer switch but am wondering if i need to switch the neutral as well?

Thanks
_________________________
Be kind to your neighbor, he knows where you live

Top
Work Gear for Electricians and the Trades
#203696 - 10/19/11 10:27 PM Re: manual transfer switch and neutral [Re: Niko]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
The electrical system needs the neutral to be grounded at 1 and only 1 point.

If both your normal Service and your generator have grounded neutrals, when they are connected together you will have the neutral of the system grounded at 2 points, which is a no-no.

If your generator neutral is grounded, you need to switch the neutral; if your generator neutral is not grounded, you can allow it to be connected to the normal system's ground via the system's neutral.
_________________________
Ghost307
Top
#203697 - 10/19/11 11:44 PM Re: manual transfer switch and neutral [Re: Niko]
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
Thanks Ghost,
they (the customer) will be installing a portable generator until a permanent one can be purchased.

Are neutrals usually grounded on the portable units? or it varies? and if it is grounded can i disconnect the neutral from the generator frame? Or i am messing up the listing?

_________________________
Be kind to your neighbor, he knows where you live

Top
#203698 - 10/20/11 12:48 AM Re: manual transfer switch and neutral [Re: Niko]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
There is usually a comment in the instructions of how to lift the bond in the generator if you are making this a non-SDS.
(not switching the neutral). I think Hondas come floating and most others are bonded from the factory.
_________________________
Greg Fretwell
Top
#203703 - 10/20/11 07:32 AM Re: manual transfer switch and neutral [Re: gfretwell]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
Iíve never switched a neutral on a resi transfer switch, whether automatic or manual. I just make the appropriate change to the ground connection at the generator itself.

Top
#203705 - 10/20/11 08:07 AM Re: manual transfer switch and neutral [Re: Niko]
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
OK. Thanks.

i think now my question turns to SDS. why would would someone choose not to remove the neutral. or any advantage of SDS or non- SDS?

i know the definition of SDS but i dont think i have a 100% grasp as to why you would have one or wouldn't.

_________________________
Be kind to your neighbor, he knows where you live

Top
#203707 - 10/20/11 09:39 AM Re: manual transfer switch and neutral [Re: Niko]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I can't think of any good reason to create an SDS in 120/240v systems. Usually you apply this when you would be changing from delta to wye or some other significant system change.
_________________________
Greg Fretwell
Top
#203708 - 10/20/11 09:41 AM Re: manual transfer switch and neutral [Re: Niko]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
Check with your POCO. a few years ago, I saw a commercial for another POCO and they had a shot on a xfer switch and wasn't switched. I contacted them and they said they didn't want the neutral switch
_________________________
"Live Awesome!" - Kevin Carosa
Top
#203710 - 10/20/11 09:43 AM Re: manual transfer switch and neutral [Re: Niko]
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
OK thank you for the replies.
_________________________
Be kind to your neighbor, he knows where you live

Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 43 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals