#203549 - 10/07/11 08:33 PM Article 410.10 D
sparkync Offline
Member
Registered: 10/17/02
Posts: 809
Loc: NC
I have a customer who wants to put a chandelier over the jecuzzi in the master bath. According to Article 410.10 D
of the 2011 code, it can't be within 3 ft. horizontally of the bathtub rim or 8ft. vertically, and it has to be marked for damp locations. What is your interpretation of putting the chandelier out 3ft. from the jecuzzi, and still mounted on an 8ft. ceiling? Does the 8ft. rule still apply if it's not over the jecuzzi? Thanks for your input. Also, they may have a problem finding a chandelier marked for damp locations. Thanks again.. Steve
Top
2017 / 2014 NEC & Related Books and Study Guides
#203550 - 10/08/11 01:15 AM Re: Article 410.10 D [Re: sparkync]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
They are talking about a restrictive box 8' high and 3' wide above the rim and out from the tub.

If you are more than 3' out from the tub or more than 8' above the rim to any part of the fan or light, you are out of the box.

_________________________
Greg Fretwell
Top
#203552 - 10/08/11 10:17 AM Re: Article 410.10 D [Re: sparkync]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 899
Loc: Chicago Illinois USA
As I recall that 8' above the rim measurement is made to the lowest point of the light, not to the box that it's mounted to.

Be sure to check for any local Amendments.
Some of the suburbs around here require that it also be fed protected by a GFI circuit; and there's one that prohibits it being mounted above the tub no matter how high it is.
_________________________
Ghost307
Top
#204037 - 11/04/11 10:18 PM Re: Article 410.10 D [Re: sparkync]
mikethebull Offline
Member
Registered: 03/18/07
Posts: 100
Loc: Rhode Island
ghost 307 is right the 8 ft. measurement is from the finished fixture.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 37 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals