The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm≤ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 292 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#203537 - 10/07/11 06:37 AM Grounding Question
wire_twister Offline
Member

Registered: 07/25/07
Posts: 265
Loc: Georgia USA
Alright fellas, my partner and I were roughing in a new house last week, and I noticed that the rebar sitcking out of the footing for us to bond to was the epoxy coated stuff. Does this coating on the rebar decrease its effectiveness when used as a ufer? I can and did grind the coating off where my clamp is at, but it got me to wondering about the part that is in the concrete. As far as my AHJ, I could bond this rod or not, he just wants to see 2 8 foot rods bonded together and hooked in the meter pan. What do you think?
_________________________
Jimmy

Life is tough, Life is tougher when you are stupid

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#203541 - 10/07/11 08:56 AM Re: Grounding Question [Re: wire_twister]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
You are not allowed to use epoxy-coated rebar to make an electrode.

Top
#203542 - 10/07/11 10:18 AM Re: Grounding Question [Re: wire_twister]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
That should have failed the footer inspection. That is when the Ufer rough is done here. It is usually done by the structural inspector but he is supposed to know better. Typically what happens here with epoxy rebar is you get a complete 20' stick of bare rebar in the bottom of the pour and another 20' stick bent up into the wall and the remaining 15' or so tied to the 20' in the hole with a bunch of bow ties.
Most of the time the whole footer is uncoated rebar. 2 loops of #5 (continuous).
_________________________
Greg Fretwell

Top
#203543 - 10/07/11 12:16 PM Re: Grounding Question [Re: wire_twister]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Same here in NJ, Building Inspector does footing inspection & UFER connection to rebar. I don't think epoxy coated rebar is used for footing/foundations in resi. I see a lot on highway construction, and large structures.
_________________________
John

Top
#203553 - 10/08/11 05:00 PM Re: Grounding Question [Re: HotLine1]
sparky Offline
Member

Registered: 10/18/00
Posts: 5542
theoretically, more bonding to a ufer is better

i often wonder if it's possible to calculate the R value , expoxy or no.......~S~

Top
#203554 - 10/08/11 09:12 PM Re: Grounding Question [Re: wire_twister]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
Iíd say it looks like you donít have much choice now but to use the two 8-foot ground rods anyway. Itís too bad, since all the concrete guy really needed to do was roll out a lousy 20-feet of #4 Cu in the footing before he poured it and just leave a tail for you to connect to and everything would have been fine. Instead the building owner is stuck with the crappy rods and some #6 Cu for a grounding electrode.

Top
#203555 - 10/08/11 09:55 PM Re: Grounding Question [Re: wire_twister]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
If they haven't back filled the outside walls you might be able to do a ground ring but the price of copper makes that pretty expensive.
_________________________
Greg Fretwell

Top
#203556 - 10/08/11 10:03 PM Re: Grounding Question [Re: wire_twister]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
My 'OOPS'.

Assumed plastic water pipe. did the 2 rods(builder does not use rebar), then suddenly 650' of 1" copper water pipe shows up!

Meter and panel on the left rear,in the garage, W-main is in the right front.

140' later,it is bonded.

Which leads me to a question:
200A #4 to the grd rods. Do I need #4 to the water main? or is that now a bond and # 6 will do?

(I ran #4 already- Ouch)

Never assume! frown

Top
#203557 - 10/08/11 10:08 PM Re: Grounding Question [Re: wire_twister]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
Actually you have it backward and got lucky. You do need #4 to the pipe and #6 to the rods ... and you need both so you are in compliance. It's Miller Time.
_________________________
Greg Fretwell

Top
#203558 - 10/08/11 10:27 PM Re: Grounding Question [Re: gfretwell]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Originally Posted By: gfretwell
Actually you have it backward and got lucky. You do need #4 to the pipe and #6 to the rods ... and you need both so you are in compliance. It's Miller Time.



Ha,HA!!

Lucky in a strange way!

I figured #4 for the water main, I know the rods are supplemental.
First time in this town and they require copper water mains.
Live and learn. I knew where the main was coming in but the pipe showed up 2 weeks after the power was on.

AAAARRRgg.


Edited by leland (10/08/11 10:29 PM)