#203328 - 09/21/11 11:41 PM Staircase Pressurization Fan Motor Overload
sccat Offline
Member
Registered: 06/24/05
Posts: 14
Loc: CHN
Is there a Thermal Relay in a DOL starter for "staircase pressurization fan"?
When motor overload happens,will the Thermal Relay cut off the contactor?
Top
Work Gear for Electricians and the Trades
#203336 - 09/22/11 02:55 PM Re: Staircase Pressurization Fan Motor Overload [Re: sccat]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Your second question: Thermal OLs 'open', and the motor starter opens (Off).

First question may require more than the NEC, as staircase pressurization is Building & Fire Safety Codes. I suggest that you contact the local AHJs in whatever area you are working in. My opinion would be no OLs, just short circuit protection as this is a life safety item, perhaps like a fire pump. Just my opinion.

_________________________
John
Top
#203396 - 09/26/11 09:57 PM Staircase Pressurization Fan Motor Overload
sccat Offline
Member
Registered: 06/24/05
Posts: 14
Loc: CHN
Is there a Thermal Relay in a DOL starter for "staircase pressurization fan"?
When motor overload happens,will the Thermal Relay cut off the contactor?
Top
#203397 - 09/26/11 10:20 PM Re: Staircase Pressurization Fan Motor Overload [Re: sccat]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
Only ONCE did I have to build such a circuit.

The AHJ determined that such a blower is NOT a life essential device.

So the OL heaters were left in place.

-----

Each situation is going to be a Life Safety issue. It's outside the NEC.

----

WRT smaller ( 1hp or less ) thermal overloads lead directly to integral drop-out from the load.

Not uncommonly, they reset, automatically, when the temp drops they re-trigger. They DO NOT interact with any contactor what so ever.

These beasties interrupt line current -- and then restore it.

These motors are so small that contactors are uncommon.

_________________________
Tesla
Top
#203402 - 09/27/11 03:45 AM Re: Staircase Pressurization Fan Motor Overload [Re: sccat]
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Originally Posted By sccat
Is there a Thermal Relay in a DOL starter for "staircase pressurization fan"?
When motor overload happens,will the Thermal Relay cut off the contactor?


In a Direct On Line starter, your only real protection is thermal via the overloads at the base of the contactor.
This should by rights open the control circuit and shut everything off, unless it has been poorly designed or wired.

This is first year apprentice stuff, why do you ask?
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#203404 - 09/27/11 06:10 AM Re: Staircase Pressurization Fan Motor Overload [Re: sccat]
sccat Offline
Member
Registered: 06/24/05
Posts: 14
Loc: CHN
Some people think that "staircase pressurization fan" is a Life Safety Equipment as "fire pump".
Top
#203406 - 09/27/11 06:34 AM Re: Staircase Pressurization Fan Motor Overload [Re: sccat]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Sccat:

You have this posted in the NEC section from 9/22/2011, which has one response. I'll merge the two together.

You're right!! Now, it will depend on 'who' the 'some people' are!!

The best solution I would suggest is to speak to the local AHJ about this. IF the ventilation system is considered 'life safety' or not.


Edited by HotLine1 (09/27/11 06:36 AM)
Edit Reason: prep to merge
_________________________
John
Top
#203408 - 09/27/11 08:51 AM Re: Staircase Pressurization Fan Motor Overload [Re: sccat]
sccat Offline
Member
Registered: 06/24/05
Posts: 14
Loc: CHN
NFPA 92A-2006 Standard for Smoke-Control Systems Utilizing Barriers and Pressure Differences

Annex D Fire Fighters’ Smoke-Control Station Considerations

Control actions issued from the FSCS should not override or bypass devices and controls intended to protect against electrical overloads, provide for personnel safety, and prevent major system damage.

Is "Staircase Pressurization Fan " a part of "Smoke-Control Systems"?
Top
#203409 - 09/27/11 11:58 AM Re: Staircase Pressurization Fan Motor Overload [Re: sccat]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Again, I say...talk to the local AHJ!

BTW, you profile states your location as "CHN", would you care to elaborate on that please?

_________________________
John
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 52 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals