The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Today at 04:48 AM
Temporarily feeding a panel...
by Potseal
Yesterday at 11:05 PM
Massive power outage South Australia
by Meadow
Yesterday at 06:46 AM
short circuit??
by Meadow
Yesterday at 06:43 AM
Norwegian power?
by Meadow
Yesterday at 06:36 AM
New in the Gallery:
12.5A through 0.75mm≤ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
Potseal 7
sparky66wv 7
Who's Online
0 registered (), 282 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#203327 - 09/21/11 06:18 PM generator transfer switch
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
I am planning on installing a manual transfer switch (200A) for a standby residential generator. The transfer switch will be immediately after the main 200Amp disconnect. My question is do i need to have a fused or non-fused transfer switch. Please provide NEC reference so i will learn and know for future.

Thanks for the replies
_________________________
Be kind to your neighbor, he knows where you live


Top
2014 / 2011 NEC & Related Books and Study Guides
#203329 - 09/22/11 07:58 AM Re: generator transfer switch [Re: Niko]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
It will have alot to do with which code revision you are under and local code. I'm out of the office and way from me code books as long as you wire the switch as a 200 and switch all the way through you generator panel then I don't see a need for additional OCPD's. It's protected.

A little side note with my inspector cap on, its my humble opinion even though it sounds like you are just doing an add on, it has to meet current code. I do belive in the 2008 cycle requires an automatic switch, not manual
_________________________
"Live Awesome!" - Kevin Carosa

Top
#203330 - 09/22/11 08:24 AM Re: generator transfer switch [Re: Niko]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
We are under the 2008 NEC and it seems Manual switch is allowed. The main service is 200Amps but the portable generator is rated at 50Amps. I am installing 200Amp switch for future capability.
_________________________
Be kind to your neighbor, he knows where you live


Top
#203334 - 09/22/11 02:46 PM Re: generator transfer switch [Re: Niko]
KJay Offline
Member

Registered: 11/27/07
Posts: 763
Loc: MA, USA
If itís a 200A transfer switch on the load side of the 200A service disconnecting means, I donít see why it would need to be fused, especially if its service rated and sized for the full load.
I donít see anything the NEC that would require it either and I have never been required to install a fused transfer switch on a residence before. The generators Iíve installed all had their own built in OCP, which was rated lower than the maximum rating of the transfer switch.

Top
#203335 - 09/22/11 02:48 PM Re: generator transfer switch [Re: Niko]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6786
Loc: Brick, NJ USA
Niko:

Ditto to what Kjay said above. OCP before xfr switch & full rated & service rated...no issues.
_________________________
John

Top
#203338 - 09/22/11 04:25 PM Re: generator transfer switch [Re: Niko]
Niko Offline
Member

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
I appreciate your replies.