#203327 - 09/21/11 06:18 PM generator transfer switch
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
I am planning on installing a manual transfer switch (200A) for a standby residential generator. The transfer switch will be immediately after the main 200Amp disconnect. My question is do i need to have a fused or non-fused transfer switch. Please provide NEC reference so i will learn and know for future.

Thanks for the replies
_________________________
Be kind to your neighbor, he knows where you live

Top
2017 / 2014 NEC & Related Books and Study Guides
#203329 - 09/22/11 07:58 AM Re: generator transfer switch [Re: Niko]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
It will have alot to do with which code revision you are under and local code. I'm out of the office and way from me code books as long as you wire the switch as a 200 and switch all the way through you generator panel then I don't see a need for additional OCPD's. It's protected.

A little side note with my inspector cap on, its my humble opinion even though it sounds like you are just doing an add on, it has to meet current code. I do belive in the 2008 cycle requires an automatic switch, not manual
_________________________
"Live Awesome!" - Kevin Carosa
Top
#203330 - 09/22/11 08:24 AM Re: generator transfer switch [Re: Niko]
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
We are under the 2008 NEC and it seems Manual switch is allowed. The main service is 200Amps but the portable generator is rated at 50Amps. I am installing 200Amp switch for future capability.
_________________________
Be kind to your neighbor, he knows where you live

Top
#203334 - 09/22/11 02:46 PM Re: generator transfer switch [Re: Niko]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
If itís a 200A transfer switch on the load side of the 200A service disconnecting means, I donít see why it would need to be fused, especially if its service rated and sized for the full load.
I donít see anything the NEC that would require it either and I have never been required to install a fused transfer switch on a residence before. The generators Iíve installed all had their own built in OCP, which was rated lower than the maximum rating of the transfer switch.
Top
#203335 - 09/22/11 02:48 PM Re: generator transfer switch [Re: Niko]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Niko:

Ditto to what Kjay said above. OCP before xfr switch & full rated & service rated...no issues.

_________________________
John
Top
#203338 - 09/22/11 04:25 PM Re: generator transfer switch [Re: Niko]
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
I appreciate your replies.

Learning never exhausts the mind.
_________________________
Be kind to your neighbor, he knows where you live

Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 37 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals