The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm≤ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 327 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#203227 - 09/15/11 09:58 AM 175kw Generator grounding
Micmann Offline

Registered: 04/22/05
Posts: 20
I have a set of drawings from an engineer for a 175kw 120/240 single phase generator. In the drawing he has two ground rods at the generator and bonds the rods and the generator with 4/0 copper. He then shows the 4/0 copper running to the structure and bonding at the structure main/ATS (the main and ATS will be in one unit) with the grounding system. From the breaker in the generator he has two paralleled 1/0 running with the generator feeders as equipment grounds. My question is does the 4/0 from the rods and generator casing need to run to the structure grounding system? Isnít the generator breaker the first disconnecting means and if the neutral and ground are bonded together in the generator doesnít the paralleled 1/0ís satisfy the grounding of the structure not needing the 4/0 to be run all the way to the ATS? Iím not asking to doubt the engineer. Itís mostly for my own knowledge for future installations to make sure Iím not missing something I donít understand.


2014 / 2011 NEC & Related Books and Study Guides
#203231 - 09/15/11 10:56 AM Re: 175kw Generator grounding [Re: Micmann]
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
The grounding conductors are all going to be bonded together. The only question is how you deal with the grounded (neutral) conductor. That will depend on whether it is switched in the transfer equipment.
The ultimate goal is that you only have one main bonding jumper in the system in either condition (utility or generator)