Can anyone please help me understand the purpose/meaning behind this article?
Top
2017 / 2014 NEC & Related Books and Study Guides
#203228 - 09/15/11 10:41 AM Re: Clarification needed on Article 200.3 [Re: Helectric]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Looks to me that they are saying "no neutral in with the service, no neutral allowed inside the building." Guess they don't want you to count on the loads being perfectly balanced, or using the ground rod instead of a neutral.

Keep in mind that the NEC is attempting to address EVERY scenario. For example, the mill I'm at today is fed by the PoCo with three high-voltage 'hots.' There's no neutral from the PoCo. This means that we need a transformer to 'create' that neutral.

A lot of wells and pump houses are served by 'corner grounded' 3-phase power. If you want to have a neutral in that pump house, you'll need a transformer .... even if it's a "240 to 240" transformer.

After all, the electricity can't "go home" if the neutral wire doesn't go all the way back to the source.
Top
#203230 - 09/15/11 10:52 AM Re: Clarification needed on Article 200.3 [Re: Helectric]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
This is what the handbook comment says.

Quote:
Grounded conductors of premises wiring must be connected to the supply system (service or applicable separately derived system) grounded conductor to ensure a common, continuous, grounded system.
_________________________
Greg Fretwell
Top
#203283 - 09/18/11 07:16 PM Re: Clarification needed on Article 200.3 [Re: Helectric]
mikethebull Offline
Member
Registered: 03/18/07
Posts: 100
Loc: Rhode Island
It is telling the installer that if you run a neutral ( grounded ) conducter you must terminate that conducter
Top
#203291 - 09/19/11 11:39 AM Re: Clarification needed on Article 200.3 [Re: Helectric]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
See 250.24 C
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals