The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
42 minutes 17 seconds ago
Re: Fabricating Guards out of Lexan?
by frank
Today at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Today at 01:26 PM
Why cables look like they do
by Texas_Ranger
Today at 12:33 PM
100% breakers?
by Texas_Ranger
Yesterday at 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 20
Webmaster 16
Trumpy 12
ghost307 12
frank 11
Who's Online
1 registered (Webmaster), 0 Guests and 66 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#203226 - 09/15/11 09:27 AM Clarification needed on Article 200.3
Helectric Offline
Member

Registered: 01/07/05
Posts: 91
Loc: Brandon, SD
Can anyone please help me understand the purpose/meaning behind this article?

Top
2017 / 2014 NEC & Related Books and Study Guides
#203228 - 09/15/11 10:41 AM Re: Clarification needed on Article 200.3 [Re: Helectric]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Looks to me that they are saying "no neutral in with the service, no neutral allowed inside the building." Guess they don't want you to count on the loads being perfectly balanced, or using the ground rod instead of a neutral.

Keep in mind that the NEC is attempting to address EVERY scenario. For example, the mill I'm at today is fed by the PoCo with three high-voltage 'hots.' There's no neutral from the PoCo. This means that we need a transformer to 'create' that neutral.

A lot of wells and pump houses are served by 'corner grounded' 3-phase power. If you want to have a neutral in that pump house, you'll need a transformer .... even if it's a "240 to 240" transformer.

After all, the electricity can't "go home" if the neutral wire doesn't go all the way back to the source.

Top
#203230 - 09/15/11 10:52 AM Re: Clarification needed on Article 200.3 [Re: Helectric]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9060
Loc: Estero,Fl,usa
This is what the handbook comment says.

Quote:
Grounded conductors of premises wiring must be connected to the supply system (service or applicable separately derived system) grounded conductor to ensure a common, continuous, grounded system.
_________________________
Greg Fretwell

Top
#203283 - 09/18/11 07:16 PM Re: Clarification needed on Article 200.3 [Re: Helectric]
mikethebull Offline
Member

Registered: 03/18/07
Posts: 101
Loc: Rhode Island
It is telling the installer that if you run a neutral ( grounded ) conducter you must terminate that conducter

Top
#203291 - 09/19/11 11:39 AM Re: Clarification needed on Article 200.3 [Re: Helectric]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
See 250.24 C

Top