#203202 - 09/14/11 10:52 AM Will a 240v window air conditioner run OK on 208V?
Helectric Offline
Member
Registered: 01/07/05
Posts: 90
Loc: Brandon, SD
Any thoughts or experience with this?
Top
Work Gear for Electricians and the Trades
#203203 - 09/14/11 11:17 AM Re: Will a 240v window air conditioner run OK on 208V? [Re: Helectric]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
My bet is no but the answer will be on the label.
_________________________
Greg Fretwell
Top
#203205 - 09/14/11 11:46 AM Re: Will a 240v window air conditioner run OK on 208V? [Re: Helectric]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
If the nameplate say 240 .... no, it won't run properly.

If the nameplate REALLY says 230, you can run it at exactly 208. Any voltage drop at all and you're SOL.

If it says 220, you're good to go.
Top
#203210 - 09/14/11 12:47 PM Re: Will a 240v window air conditioner run OK on 2 [Re: Helectric]
wa2ise Offline
Member
Registered: 11/29/02
Posts: 782
Loc: Oradell NJ USA
In theory, a boost transformer would solve the problem, by raising the 208V to 240V. Something like this place (no affiliation, others may have better product) http://www.transformeronline.com/buckboost.htm

Being code may be an issue.
Top
#203211 - 09/14/11 04:05 PM Re: Will a 240v window air conditioner run OK on 2 [Re: Helectric]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
I'm unaware of ANY recent HVAC equipment whose motors couldn't tolerate 200-230 nominal, delivered voltages.

More current will be drawn at the reduced voltage.

The big issue for many HVAC systems is not the motor -- but the control power transformer.

Many are multi-tap -- in which case re-tapping would be most wise.

Unlike the motor, the control logic is pretty finely dialed in.
_________________________
Tesla
Top
#203213 - 09/14/11 04:40 PM Re: Will a 240v window air conditioner run OK on 2 [Re: Tesla]
Vindiceptor Offline
Member
Registered: 03/28/11
Posts: 98
Loc: San Diego
Originally Posted By Tesla
I'm unaware of ANY recent HVAC equipment whose motors couldn't tolerate 200-230 nominal, delivered voltages.

More current will be drawn at the reduced voltage.

The big issue for many HVAC systems is not the motor -- but the control power transformer.

Many are multi-tap -- in which case re-tapping would be most wise.

Unlike the motor, the control logic is pretty finely dialed in.


230 rated single phase motors will run at 208 volts, but will probably not last long (more than a few weeks or months) before they burn up.

I'd also question whether a 'window' unit will have any control transformer multi-tap ability, it might though, it seems some of the newer units are dual rated.


Edited by Vindiceptor (09/14/11 04:45 PM)
Top
#203214 - 09/14/11 05:08 PM Re: Will a 240v window air conditioner run OK on 2 [Re: Helectric]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6775
Loc: Brick, NJ USA
Just my opinion, but...why not just get a window unit that is rated for nominal 208 volts?

Yes, you can install a buck-boost transformer onto the AC circuit back by the panel, but IMHO the labor and materials will probably be $$$ more than another AC; unless we are talking about a really 'big' window unit.

_________________________
John
Top
#203216 - 09/14/11 06:35 PM Re: Will a 240v window air conditioner run OK on 2 [Re: Helectric]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
230 rated single phase motors will run at 208 volts, but will probably not last long (more than a few weeks or months) before they burn up.

Virtually all small motors made in the last thirty years will ENTIRELY tolerate 200-230 VAC nominal -- its even on their name-plate.

You have to get into larger ( industrial ) sizes before it's an issue.

And, yes, I've installed 240VAC 1 phase HVAC units where only 208VAC power was available. Six years later the units were still running strong.

The HVAC industry has standards -- one of which is to make it possible to run their equipment at both voltages.

There are NO END of apartments out their receiving two legs of 208Y120 power. Ditto for small businesses.

It is in the nature of small hermetic A/C systems for them to operate entirely surrounded by refrigerant -- and to actively reject their heat to the outside.

Their motors can take it, and take it, and take it.



Edited by Tesla (09/14/11 06:37 PM)
_________________________
Tesla
Top
#203217 - 09/14/11 07:58 PM Re: Will a 240v window air conditioner run OK on 2 [Re: Helectric]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
I just looked a couple up on the internet (LG and Frigidaire) they say 230/208v.

The real answer is going to be on the nameplate of the one in question but it looks like Tesla is right on.
_________________________
Greg Fretwell
Top
#203221 - 09/14/11 11:26 PM Re: Will a 240v window air conditioner run OK on 2 [Re: Helectric]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
I'm with Tesla on this - but I wouldn't even look for taps on a window AC, if they have a transformer. The motor has overload protection and undervoltage probably won't hurt the controls.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 20 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals