The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 301 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#203060 - 09/06/11 09:20 PM water damage on lugs and buss
falcondfb Offline
Member

Registered: 09/28/02
Posts: 37
Loc: Jersey, USA
We have been busy the last week getting power restored to people in northern new jersey. I have a couple of homes with damage to the panel buss because the panels were energized. we are just going to replace them. Today we went to a commercial property with a 1200 amp 3 phase switch gear where the feeders lands on lugs at the end of the buss. The service was hot under water and now have white corrosion on them. the buss has rust and obvious signs that it was under water. I am no engineer so what is the typical course of action in dealing with this issue??

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#203061 - 09/06/11 09:29 PM Re: water damage on lugs and buss [Re: falcondfb]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Falcon:

You can read the NEMA reccomendations here on this link:

http://www.nema.org/stds/water-damaged.cfm

It's not NEC verbatum, but....remember 110.3 (b) (Mfg instructions)

Resi stuff is trashed basically. Large comm/ind gear may be 'factory' (mfg) certified as refurbished. Factory costs and timeline vs. replacement $$ are an important factor.

based on your description, lugs are replacable.....buss is an an issue.
_________________________
John

Top
#203062 - 09/06/11 09:35 PM Re: water damage on lugs and buss [Re: falcondfb]
falcondfb Offline
Member

Registered: 09/28/02
Posts: 37
Loc: Jersey, USA
wow you are quick. I just came across that link in another post and didn't get back in time to say so. It looks like a call to the mfg is in order.

Thank you for the quick response, again

Top
#203063 - 09/06/11 10:42 PM Re: water damage on lugs and buss [Re: falcondfb]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
If the bus is Al I'd expect it to be totally trashed.

If copper...?

I'd expect that either way -- it's going to be replaced.

That level of flooding normally requires gutting.

Flood damage that high had to effect a lot more than just the Service.
_________________________
Tesla

Top
#203609 - 10/12/11 07:51 PM Re: water damage on lugs and buss [Re: falcondfb]
mikethebull Offline
Member

Registered: 03/18/07
Posts: 101
Loc: Rhode Island
There was a lot of homeowners last year that wanted electricians to "sign-off" on houses that were flooded out in the big rains. This was due to the insurance companies.
"

Top
#203611 - 10/13/11 01:07 AM Re: water damage on lugs and buss [Re: mikethebull]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8530
Loc: SI,New Zealand
What I'd be more concerned about is not the lugs themselves, but the wires connected to them.
Having water get into any sort of wiring where it is terminated at a lug (or whatever), can cause water to move up under the cable insulation (by capillary effect), this can then cause a failure later on as the wire corrodes from the inside out.

I myself would be rather hesitant in re-connecting anything that has been submerged, without a VERY good megger and continuity test being done on the the whole place.
Let alone certify it as safe.
Be very careful here, it could come back to bite you in the britches. eek
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#203619 - 10/13/11 11:29 AM Re: water damage on lugs and buss [Re: falcondfb]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Mike:
I share your opinion. Wiring that is submerged, or been subject to 'water damage' has to be replaced. The effects of corrosion or other internal damage cannot be 'seen' and will rear its head eventually.

I didn't mention anything regarding the conductors to the OP, as he only seemed to have concerns about the gear. Perhaps a 'bad' on my part?
_________________________
John

Top
#203634 - 10/13/11 09:27 PM Re: water damage on lugs and buss [Re: falcondfb]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
There are some companies out there who will take the time and try to clean out all of the service gear to see if it is fit to re-use. As long as I get a letter from them stating that it is OK to turn back on, that letter goes into the file for reference.

Top
#203641 - 10/14/11 06:26 PM Re: water damage on lugs and buss [Re: falcondfb]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Harold:
You are talking commercial (large) gear, not resi, right?
_________________________
John

Top
#203642 - 10/15/11 03:18 PM Re: water damage on lugs and buss [Re: falcondfb]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
I can't imagine any circumstance whereby a commercial property could purchase fire insurance upon a property that's been flooded and then re-energized.

Period.

The debris that comes with a flood ruins everything. Things like MAINS circuit breakers.

It all has to go back to the factory for a rebuild. The active components are going to be toast.

Floods are disasters, plain and simple.

You can't fox your way around it.