The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (ampherder), 184 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#202937 - 09/02/11 03:41 AM Service to a detached building
lite bulb Offline
Member

Registered: 02/12/06
Posts: 77
Loc: wilm,de.
I'm installing a service to a detached building, main building is 480/277 the detached bulding will be feed from the main building and then step down to 120/208 do I have to carry a neutral and ground to the detached building.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#202943 - 09/02/11 10:30 AM Re: Service to a detached building [Re: lite bulb]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Where's the 480/208 transformer? Are you keeping the neutral for the 277 isolated from the neutral for the 120 isolated from each other in the transformer?

No matter what you do, you need a ground wire between the buildings, and a grounding electrode at the detached building as well.

IMO, you should keep the 277 neutral apart from the 120 neutral at the transformer. Indeed, I see no reason to bring the 'gray' neutral in with the transformer feed at all. This makes the transformer a 'separately derived service'.

[red] ECN regulars double-check me on this: [/red]
With a separately derived service, the first breaker after the transformer becomes the point where you separate your grounds from your neutral, just as with your service from the PoCo. You'll want to use bonding bushings on your connectionc between the transformer and that breaker.

Top
#202946 - 09/02/11 11:02 AM Re: Service to a detached building [Re: lite bulb]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
If you bring the feeder to the second building as a 480 delta and set the transformer in the second building, I agree with Reno. This becomes a SDS and your neutral starts there. That is probably the best way to do it anyway, saving wire and reducing I2R losses. Establish your ground electrode system just like a service entrance.
_________________________
Greg Fretwell

Top
#202956 - 09/02/11 02:23 PM Re: Service to a detached building [Re: lite bulb]
lite bulb Offline
Member

Registered: 02/12/06
Posts: 77
Loc: wilm,de.
thanks for your reply guys

Top
#203006 - 09/04/11 07:40 PM Re: Service to a detached building [Re: lite bulb]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
I do the same way as Reno and Greg expain just run delta to detached building then treat them as SDS however pay attetion to the delta connection I know some area may required a CGD { Corner Grounded Delta } that can get tricky if not heeded with connections.

The CGD is only used if you have CGD in main service otherwise just run full delta as those guys mention.

Merci,
Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#203009 - 09/04/11 08:35 PM Re: Service to a detached building [Re: lite bulb]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
You've missed the big issue: does the customer intend to utilize 480Y277 circuits in the dependent building.

Having actually run circuits identical to your proposal -- we ended up pulling a neutral for a 480Y277 Panel -- which was tapped to create a SDS 208Y120 system.

Reno: there is no 480:208 transform.

H1-H2 = 480V
X1-Xo = 120V

The turns ratio is 4:1...

208V arrises as a consequence of adding two legs of 120V power -- adjusting for their phase angle difference.

The 208Y120 system lags the 480Y120 by 30 degrees -- at all times.

The additional conductor expense ( the High Board ) is balanced by using 277V lighting -- especially if site runs are a consequence of the new building.

A bonding run, properly sized, is required -- of course.

A Ufer for the new building is required -- by my AHJ -- ground rods don't cut it out my way.

We stay away from Corner Grounded Deltas. If the primary Service is 480Y277 -- which our Poco insists upon -- then Grounding a 277 leg would induce some horrific ground currents.

I've actually seen that happen -- by accident. A dedicated fire pump Service was corner grounded. It drew 90Amps on that leg -- at 277Volts.

Yiikes.

Fortunately, I'd bonded everything in sight -- so no one died. ( Particularly, me. I became a 'bird on a wire.' )

Your Low Board is going to have to have a properly sized C/B -- else you'll have to tack on a Safety Switch right at the XFMR -- and bonding bushings are required on all of the dependent Low Board raceways -- until you hit the OCPD.

It all sounds like a lot of fun.


Edited by Tesla (09/04/11 08:37 PM)
_________________________
Tesla

Top
#203048 - 09/06/11 11:18 AM Re: Service to a detached building [Re: lite bulb]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Nonsense, Tesla. I know I've put in transformers that had 480 (three phase) going in, and 208/120 coming out. Indeed, I can't see any way to create 240/120 in a "Wye" configuration at all.

True, I did ASSUME the OP was talking about a 3-phase transformer - which, technically, is three transformers in one box.