The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
0 registered (), 198 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#202677 - 08/21/11 11:59 AM Tankless Hotwater heater
dougwells Offline


Registered: 05/03/03
Posts: 1226
Loc: kamloops BC Canada
I have an inquiry about installing a circuit for this Item.
Will this need a sub panel and am a bit rusty about the feeder size for the a sub panel.
Has anyone installed on of these thanks.
This will be a renovation

2014 / 2011 NEC & Related Books and Study Guides
#202678 - 08/21/11 07:54 PM Re: Tankless Hotwater heater [Re: dougwells]
Tesla Offline

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
"3 x 50 AMP breakers (depends on local codes)"

Each breaker at 240 VAC

"Minimum 3 x #8 AWG Copper (depends on local codes)"

So you'll need at least #8 -- but more likely #6 conductors.

(I'm assuming that you'll be dealing with a 60 degree panel board and or are using Romex. Otherwise, you'd be able to use #8.)


I've never installed such a beast.

Instead I've installed insta-hots 30A @ 208 or 277...

You'll have to deal with line-of-sight disconnecting means -- which normally is addressed by a sub-panel rated 150 Amps @240VAC.

You can pipe and wire the feeder -- or use MC -- they make it big, BTW.

MC is available all the way up to 705 kCMIL. (!)

#202679 - 08/21/11 08:54 PM Re: Tankless Hotwater heater [Re: dougwells]
jay8 Offline

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
I am a little suprised at the electrical layout. The manufacturer is suggesting three breakers to a single control panel. How do you effectively isolate the unit for service, normally there is a single point of isolation on the control panel such as a service switch on the front of it.

Also, from the drawing (page 13) it looks like the exposed L1/L2 terminals are right next to the inlet and outlets ports for the water piping. The drawings show wires running right past the mechanical piping within the control panel. Unusual to say the least that there seems to be no barrier between the sections.