#202141 - 07/20/11 12:15 PM floor receptacle in commercial kitchen
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Is a conduit up out of the floor supporting a box with a receptacle an acceptable installation?
(for a piece of kitchen equipment out in the middle of the floor (not near a wall))
Top
Work Gear for Electricians and the Trades
#202146 - 07/20/11 02:08 PM Re: floor receptacle in commercial kitchen [Re: cgw]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Sure, you can do it. BUT ....

Be aware that the thing will have the living daylights beat out of it as the tables get shifted about and the floor gets hosed off. Plan accordingly.

Which means ... 3/4 rigid stub-ups, a second support to keep the box from twisting, compression connectors to allow future box replacement, and cast-iron FS-type boxes (not the wimpy Bell boxes). AND have the GFCI somewhere else.
Top
#202152 - 07/20/11 04:43 PM Re: floor receptacle in commercial kitchen [Re: cgw]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
Normally pendent drops are used.

The Health Inspector will normally be your objecting party.
_________________________
Tesla
Top
#202153 - 07/20/11 05:05 PM Re: floor receptacle in commercial kitchen [Re: cgw]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
cgw:

I agree with Reno & Tesla. I would also add...check with your local AHJ first.


Edited by HotLine1 (07/20/11 05:44 PM)
_________________________
John
Top
#202157 - 07/20/11 06:55 PM Re: floor receptacle in commercial kitchen [Re: cgw]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
In the fast food business I saw a mix of the FS boxes Reno described on 3/4" RMC stub ups and pendants.
They really try to put in a stem wall with regular receptacles on them and FRP sheathing or tile for the wash down. I imagine with the GFCI requirement the pendants are even more attractive.
_________________________
Greg Fretwell
Top
#202166 - 07/20/11 08:30 PM Re: floor receptacle in commercial kitchen [Re: cgw]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
If you're using GRC and cast boxes, you'll have to use Erickson couplings if you want to make any future box replacement easier. Also, the permanent location of the box will interfere with any future rearrangement of the Kitchen.
I vote for using drops like you see at all of the McDonalds.
_________________________
Ghost307
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals