The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Ruben Rocha
Today at 07:36 PM
ESA Arc flash course
by frank
Today at 04:25 PM
Re: Fabricating Guards out of Lexan?
by frank
Yesterday at 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
Yesterday at 01:26 PM
Why cables look like they do
by Texas_Ranger
Yesterday at 12:33 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 27
HotLine1 21
Ruben Rocha 16
Trumpy 12
ghost307 12
Who's Online
3 registered (ComputerWizKid, Webmaster, sparkyinak), 0 Guests and 219 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#202060 - 07/14/11 10:03 AM 480volt lights on poles no equipment gr.
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Height min of 22ft per 210.6d.
Out of building thur manholes up pole then overhead on poles.
Ground to ist then lose ground.
PER
410.42(A)Equipment grounding conductor required (OR) be inaccessible to ubnqualified persons.
We're talking long spans here single conductors 30 ft hight.

Top
2017 / 2014 NEC & Related Books and Study Guides
#202063 - 07/14/11 10:27 AM Re: 480volt lights on poles no equipment gr. [Re: Yoopersup]
Vindiceptor Offline
Member

Registered: 03/28/11
Posts: 98
Loc: San Diego

Metallic, wood, fiberglass or concrete poles?

If metallic the EG's are required.

Top
#202064 - 07/14/11 12:13 PM Re: 480volt lights on poles no equipment gr. [Re: Yoopersup]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6831
Loc: Brick, NJ USA
Yoop:

From 2008:

"410.42 Exposed Luminaire.
(A) Exposed Conductive Parts. Exposed metal parts shall be connected to an equipment grounding conductor or insulated from the equipment grounding conductor and other conducting surfaces or be inaccessible to unqualified personnel. Lamp tie wires, mounting screws, clips, and decorative bands on glass spaced at least 38 mm (11/2 in.) from lamp terminals shall not be required to be grounded."

As Vin said...metal poles must be bonded.

_________________________
John

Top
#202067 - 07/14/11 12:42 PM Re: 480volt lights on poles no equipment gr. [Re: Yoopersup]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Wood poles

Top
#202074 - 07/14/11 06:29 PM Re: 480volt lights on poles no equipment gr. [Re: Yoopersup]
HotLine1 Offline


Member

Registered: 04/03/02
Posts: 6831
Loc: Brick, NJ USA
Case closed?