The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 263 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#202037 - 07/11/11 06:23 PM AC90 protection
mersadrad Offline
Member

Registered: 03/11/11
Posts: 27
Loc: Montreal, Quebec, Canada
I want to ask in case i dont have antishort am I alowed to use electrical tape as a protection.
_________________________
“If you don't know where you are going, any road will get you there”.

Top
2014 / 2011 NEC & Related Books and Study Guides
#202046 - 07/12/11 09:17 PM Re: AC90 protection [Re: mersadrad]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
CEC 12-610 (1) ".....bushings of insulating material or equivalent devices." But consider subrule (3) which requires the protection to be visible for inspection when cable is installed in connector or clamp. So as long as the electrical tape is installed with that in mind it should be okay. Anti-shorts are preferred because they are quicker, easy to see and more reliable.

Top
#202268 - 07/28/11 04:58 PM Re: AC90 protection [Re: mersadrad]
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Tape vs anti short? I would not permit electrical tape to replace an anti short. Tape is too susceptible to cutting by the armour of the BX and it cannot be placed in between the armour and the wire either. In fact the insulation of the wire is already more resistant to cutting than tape itself. So what use is tape in this application?

Top
#202276 - 07/29/11 10:13 AM Re: AC90 protection [Re: mersadrad]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
Mike,

My intent with referencing section 12 was just to say there is no specific reference to "anti-shorts" but it does reference insulating material or equivalent, leaving room for interpretation.

I have torn anti shorts while installing on bx, and I have always been able to wind back the armour enough that I could get several layers of tape on if needed. But I know that you are with inspections, so your post carries some weight.

Top
#202279 - 07/29/11 11:52 AM Re: AC90 protection [Re: mersadrad]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Just an FYI from 'south of the border" (2008 NEC)

320.40 Boxes and Fittings.
At all points where the armor of AC cable terminates, a fitting shall be provided to protect wires from abrasion, unless the design of the outlet boxes or fittings is such as to afford equivalent protection, and, in addition, an insulating bushing or its equivalent protection shall be provided between the conductors and the armor. The connector or clamp by which the Type AC cable is fastened to boxes or cabinets shall be of such design that the insulating bushing or its equivalent will be visible for inspection. Where change is made from Type AC cable to other cable or raceway wiring methods, a box, fitting, or conduit body shall be installed at junction points as required in 300.15.

Looks like we are basically on the same page on this.
_________________________
John

Top
#202292 - 07/29/11 10:04 PM Re: AC90 protection [Re: mersadrad]
twh Offline
Member

Registered: 03/11/04
Posts: 892
Loc: Regina, Sask.
Use red tape.

Top
#202293 - 07/29/11 11:15 PM Re: AC90 protection [Re: mersadrad]
dougwells Offline

Member

Registered: 05/03/03
Posts: 1226
Loc: kamloops BC Canada
Someone must sell the larger antishorts, but none of the suppliers here do. They just say everyone uses tape.

Top
#202314 - 07/30/11 06:19 PM Re: AC90 protection [Re: mersadrad]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Doug:
It's been awhile, but there used to be a bag of red heads attached to every roll of BX.
_________________________
John

Top
#202315 - 07/30/11 06:31 PM Re: AC90 protection [Re: mersadrad]
dougwells Offline

Member

Registered: 05/03/03
Posts: 1226
Loc: kamloops BC Canada
Yes for BX, need red heads for cable sizes #6 AWG and up smile. This cable has just a thin wrap of paper between the conductors and the sheathing btw it is an aluminum conductor cable assembly

Top