#201849 - 06/28/11 09:16 AM Overhead Three Phase 13.8 & 4160 Delta
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Overhead 13.8 & 4160 Delta no neutral present.
Running to remote building . Owners Not Utilitys.
When you come down pole to Step down Transformer where & how do you ground?
If ungrounded delta how does it trip ocp , located remotely??
Remember its Owners , Not Utlity so there Feeders!
Yoopersup
Top
2017 / 2014 NEC & Related Books and Study Guides
#201857 - 06/28/11 05:26 PM Re: Overhead Three Phase 13.8 & 4160 Delta [Re: Yoopersup]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
You ground / bond to the case of the transformer.

The OCPD trips only after the SECOND line faults to ground. That's why phase monitors are required.

Non-NEC compliant solution: Slap the foolishness out of this customer- there's no reason to preserve an ungrounded delta.
Top
#201860 - 06/28/11 05:51 PM Re: Overhead Three Phase 13.8 & 4160 Delta [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
Design By Electrical Engineer!
Phase monitors on a overhead line? 4160.
Or 13800 volts?? Please give details .
Top
#201871 - 06/28/11 09:49 PM Re: Overhead Three Phase 13.8 & 4160 Delta [Re: Yoopersup]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The medium voltage lines around my area seem to have some kind of impedance grounding going on. You see a funny looking insulator device connected to ground every so often along the line. I suspect this is just a path for lightning,
_________________________
Greg Fretwell
Top
#201874 - 06/28/11 11:35 PM Re: Overhead Three Phase 13.8 & 4160 Delta [Re: Yoopersup]
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
Originally Posted By Yoopersup
Design By Electrical Engineer!
Phase monitors on a overhead line? 4160.
Or 13800 volts?? Please give details .


Ya sérieux ??

What kind of ground fault detector you have or will set up most common in MV/HV class will have impleaded or resteror grounded or netural set up depending on the supply format is.

And you will need phase monitor to detect the ground fault on them and some case you may need automatique recloser { this part I am not too crazy but it do work very well }

Merci,
Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top

Member Spotlight
Member Since: 05/03/03
Posts: 1137
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals