The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 221 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#201673 - 06/15/11 06:05 PM mig welder
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
I have been given a mig welder to supply power for. Rated input is 230volt 20 amp single phase, but plug supplied is 50 amp 250 volt - I guess that although oversized this is just the standard welding plug, but does one wire the receptacle for the demand of the welder or the 50 amp plug supplied?

Top
2014 / 2011 NEC & Related Books and Study Guides
#201675 - 06/15/11 07:39 PM Re: mig welder [Re: jay8]
wire_twister Offline
Member

Registered: 07/25/07
Posts: 265
Loc: Georgia USA
I would wire for the demand of the welder. I have frequently run into the same thing with welders, seems there is no standard type of plug used on welders.
_________________________
Jimmy

Life is tough, Life is tougher when you are stupid

Top
#201676 - 06/15/11 07:41 PM Re: mig welder [Re: jay8]
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
Demand of the welder. It's like a range that has a 50 amp receptacle but is wired for 40 amps.

Is there a demand calculation for a welder circuit, or is it just the 80% rule?

Top
#201677 - 06/15/11 09:32 PM Re: mig welder [Re: jay8]
LarryC Offline
Member

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
As a non Electrician, I would ask the customer if they plan to upgrade to a larger power supply in the NEAR future. If so, I would use a larger conduit to allow for an easier upgrade for the next electrician, which may be you.

Top
#201678 - 06/16/11 01:32 AM Re: mig welder [Re: jay8]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Originally Posted By: jay8
I have been given a mig welder to supply power for. Rated input is 230volt 20 amp single phase, but plug supplied is 50 amp 250 volt - I guess that although oversized this is just the standard welding plug, but does one wire the receptacle for the demand of the welder or the 50 amp plug supplied?

Jay,
Welders are pretty hard on a power supply.
Is this in a residential or commercial workshop?
One thing I would note for a start is the nameplate on the welder itself, especially the Duty Cycle.
Welders with high Duty Cycles (of 60-70%) require heavier supply wiring, this is due to the weldor being able to use the welder for longer periods at a time and therefore increasing the amount of heating in the supply cabling.
If however, the welder only has a Duty Cycle of say 30-40% you can pretty much get away with a circuit that matches the current draw of the welder.
Another thing, welders and circuit breakers don't tend to go together that well, unless the CB has magnetic protection only, using a CB with thermal protection added in, will end in tears.
I've seen CB's bypassed by those that don't know any better in the past, because the wrong type of CB was installed in the first place.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#201681 - 06/16/11 09:07 AM Re: mig welder [Re: jay8]
jdevlin Offline
Member

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
26-700(2) say receptacle shall only be connected to voltage and ampere rating corresponding to the receptcle.

Is there some sort of exception for welders?

Top
#201682 - 06/16/11 09:26 AM Re: mig welder [Re: jay8]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
The welder is a pretty common Miller mig welder in a small commercial shop. Did'nt notice a duty cycle on the nameplate.

Section 42 does not seem to address this other than (42-004) letting the plug on the welder be less than the O/C rating but not less than conductor ampacity. With the price of copper these days I would want to justify the 50amp conductors.

Top
#201697 - 06/17/11 06:52 AM Re: mig welder [Re: jay8]
twh Offline
Member

Registered: 03/11/04
Posts: 898
Loc: Regina, Sask.
42-004 says that the plug can't be less than the "conductors required". That's different than the ampacity of the conductors because you can always oversize the conductors without changing plugs. If you couldn't, engineers wouldn't be able to inflate the cost of the job by going "above code".

If the size of the cord end bothers you that much, change it. Why would you run #6 wires to a load that needs a maximum 24 amp circuit ampacity?

Top
#201703 - 06/17/11 08:17 AM Re: mig welder [Re: jay8]
jdevlin Offline
Member

Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
If you put the 50 amp receptacle on a 20 amp breaker what is to prevent the user from getting a full size welder that needs 40amps and plugging it into that receptacle.

I think you either need to change the plug on the welder or put in the full 50 amp circuit.

Top
#201704 - 06/17/11 08:23 AM Re: mig welder [Re: jay8]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
Just out of curiosity I had a look at a welder from same manufacturer with twice the rated input - and same 50 amp 250 volt plug on it. And I agree, why run the #6?

So it comes out of the factory as "listed and approved" equipment with one oversized plug that fits all. I could go and change out the plug on this approved and listed piece of equipment but then I am interfering with the approval - ironic.