The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 04:10 PM
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
renosteinke 6
ghost307 6
Potseal 4
Who's Online
0 registered (), 165 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#201581 - 06/10/11 04:10 PM Installing Electric Heaters in dwelling (Art.424)
Yoopersup Offline

Registered: 03/04/03
Posts: 826
Loc: Michigan
couple Questions:
424.3 Branch circuits Allows 15/20/25/30.
Electric heat Thermostates come as high as 22 amps as far as I see. So over 20 Amps Contactor required.

Thermostate rated 125 & of load (unit Switch as disconnect 424.20) =
Off position / two poles Located per 424.19.Within sight of heater OR breaker lock on branch circuit breaker rated 125% of Load.

Another words if a Heater is Not within sight of the ther.
there must be a Fixed breaker lock on breaker feeding that circuit.

Ther. Must be 2 pole , rated 125% of load, Off position,
not over 20 amps without a contactor, within sight of heater unless breaker lock on circuit breaker.

Whatca Think Guys??

2014 / 2011 NEC & Related Books and Study Guides
#201588 - 06/10/11 08:44 PM Re: Installing Electric Heaters in dwelling (Art.424) [Re: Yoopersup]
HotLine1 Offline


Registered: 04/03/02
Posts: 6792
Loc: Brick, NJ USA

Most (if not all) BB Elec heta I installed was with LV t'stats and contactors w/12/24 volt coils. That method of control for simplicity and installation ease.

The LV t'stat & contactor always worked out to a less costly install for me, and it allowed larger loads to be controlled by a t'stst.

The answer to your question IMHO is 'Yes'...2 pole, off position, 125% rated, within site....or a breaker lockout.