#201383 - 05/30/11 01:48 AM 225.30 and generator circuits.
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
225.30(A) says you can have additional feeders or branch circuits for emergency and standby systems. Is that one per system?

If you have a generator transfer panel in building A, can you run multiple branch circuits to building B? (using up to 6 disconnects per 226.33).
_________________________
Greg Fretwell
Top
2017 / 2014 NEC & Related Books and Study Guides
#201438 - 05/31/11 08:26 PM Re: 225.30 and generator circuits. [Re: gfretwell]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Part 'a' of your inquiry...I venture yes, to one of each. In a real situation, it could be a tough sell re: 'standby' & 'emergency' details.

Part 'b' IMHO is 'yes', but I want to research more for confirmation!

This sounds like a 'George' question??
_________________________
John
Top
#201452 - 06/01/11 05:56 PM Re: 225.30 and generator circuits. [Re: gfretwell]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Meaning????

#1 It's a good question?

#2 George should respond with an answer?

If you mean the latter, I would say that the generator could serve anything you want it to with a priority to the emergency circuits. I don't know what will trigger the generator to start - hopefully the failure of the emergency circuit(s) and if there is an overload on the generator, it must be designed such that it will shed the non-emergency loads. IMHO
_________________________
George Little
Top
#201456 - 06/01/11 07:38 PM Re: 225.30 and generator circuits. [Re: gfretwell]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
George:

Meant......

#1, Yes, a good question, much like yours.

#2, Your answers are always welcome, and you are good as stirring the pot.

You make good points.

_________________________
John
Top
#201461 - 06/01/11 09:40 PM Re: 225.30 and generator circuits. [Re: gfretwell]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Load shedding was what prompted the question. If you had load management in building A controlling loads in building B, I can see why it might make things easier if you could run multiple circuits.

The more I think of it, you would probably be better off running low voltage signaling circuits to the second building and have local control but that doesn't address the original question.

Hurricane season started today so I am getting more generator questions from my friends here.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals