#201383 - 05/30/11 01:48 AM 225.30 and generator circuits.
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
225.30(A) says you can have additional feeders or branch circuits for emergency and standby systems. Is that one per system?

If you have a generator transfer panel in building A, can you run multiple branch circuits to building B? (using up to 6 disconnects per 226.33).
_________________________
Greg Fretwell
Top
2017 / 2014 NEC & Related Books and Study Guides
#201438 - 05/31/11 08:26 PM Re: 225.30 and generator circuits. [Re: gfretwell]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Part 'a' of your inquiry...I venture yes, to one of each. In a real situation, it could be a tough sell re: 'standby' & 'emergency' details.

Part 'b' IMHO is 'yes', but I want to research more for confirmation!

This sounds like a 'George' question??
_________________________
John
Top
#201452 - 06/01/11 05:56 PM Re: 225.30 and generator circuits. [Re: gfretwell]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Meaning????

#1 It's a good question?

#2 George should respond with an answer?

If you mean the latter, I would say that the generator could serve anything you want it to with a priority to the emergency circuits. I don't know what will trigger the generator to start - hopefully the failure of the emergency circuit(s) and if there is an overload on the generator, it must be designed such that it will shed the non-emergency loads. IMHO
_________________________
George Little
Top
#201456 - 06/01/11 07:38 PM Re: 225.30 and generator circuits. [Re: gfretwell]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
George:

Meant......

#1, Yes, a good question, much like yours.

#2, Your answers are always welcome, and you are good as stirring the pot.

You make good points.

_________________________
John
Top
#201461 - 06/01/11 09:40 PM Re: 225.30 and generator circuits. [Re: gfretwell]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Load shedding was what prompted the question. If you had load management in building A controlling loads in building B, I can see why it might make things easier if you could run multiple circuits.

The more I think of it, you would probably be better off running low voltage signaling circuits to the second building and have local control but that doesn't address the original question.

Hurricane season started today so I am getting more generator questions from my friends here.
_________________________
Greg Fretwell
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 102 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 10/19/00
Posts: 2724

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals