#201382 - 05/30/11 01:26 AM solar power on detached building
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
I have one pretty good question for ya North América guys someone asked me a good question related to the solar panel mounted at seperated structure or building now for the NEC code stand point they will not only required the disconnect switch at the solar panel location but also a disconnect switch at net metering location where the solar panel controller will show up { there will be two conduits running underground } so what the NEC code stand on this one ??

I know in France we have required disconnect switch at both location for detached building.

Merci.
Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
Green Building & Alternative Energy Related:
#201386 - 05/30/11 10:03 AM Re: solar power on detached building [Re: frenchelectrican]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Yes I believe you need a disconnect anywhere power enters a building.
_________________________
Greg Fretwell
Top
#201400 - 05/30/11 11:53 PM Re: solar power on detached building [Re: gfretwell]
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
Bonjour Greg.,

That what I tought so but do you have the actual art number that can be backed up ? I know the solar system they are being rewritten on codewise so I will keep my ears open on this matter and comapred what our European counterparts doing with it as well.

Merci,
Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#201403 - 05/31/11 01:07 AM Re: solar power on detached building [Re: frenchelectrican]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Does 690.13 sound like it applies to this?
That is further defined in 690.14(C)(1)
_________________________
Greg Fretwell
Top
#201596 - 06/12/11 01:08 AM Re: solar power on detached building [Re: gfretwell]
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
Originally Posted By gfretwell
Does 690.13 sound like it applies to this?
That is further defined in 690.14(C)(1)


Gregg.,

It do ring the bell to me and the [C] is the keyword I am looking for.

It almost the same what we have in France { that will be rewritten sometime next year }

Merci,
Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 20 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals