The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 11:04 PM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 6
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 234 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#201369 - 05/29/11 08:03 PM LB Fittings
MJ2000 Offline

Registered: 06/29/05
Posts: 17
Loc: Toronto, ON
Is it allowed to make joints in LB fittings?


2014 / 2011 NEC & Related Books and Study Guides
#201372 - 05/29/11 08:25 PM Re: LB Fittings [Re: MJ2000]
dougwells Offline


Registered: 05/03/03
Posts: 1226
Loc: kamloops BC Canada
I could be wrong,but I think as long as it meets the cu in box fill requirement It may be allowed.I would never splice service conductors though.
between meter and service disconnect that is. smile

#201374 - 05/29/11 08:40 PM Re: LB Fittings [Re: MJ2000]
jay8 Offline

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
I think it is something to be avoided. There is no provision for bonding in an LB, it is difficult to maintain 150mm of conductors for splicing, and some may consider an LB to be a raceway, and we know joints are not permitted within raceways.That being said I dont think there is a rule that specifically prohibits splicing in an LB.

#201414 - 05/31/11 04:24 PM Re: LB Fittings [Re: MJ2000]
mikesh Offline

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
If the conduit body has a cubic inch area marked on it then you can splice in it according to 12-3034

#201443 - 06/01/11 09:22 AM Re: LB Fittings [Re: mikesh]
jay8 Offline

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
My reading of 12-3034 is that it refers to boxes, whereas an LB would be considered a fitting - so should 12-3034 apply?

#201449 - 06/01/11 04:26 PM Re: LB Fittings [Re: MJ2000]
HotLine1 Offline


Registered: 04/03/02
Posts: 6792
Loc: Brick, NJ USA
Just a little insight from the NEC Standpoint:

314.16 (c) 2011 NEC

(2) With Splices, Taps, or Devices. Only those conduit
bodies that are durably and legibly marked by the manufacturer
with their volume shall be permitted to contain
splices, taps, or devices. The maximum number of conductors
shall be calculated in accordance with 314.16(B). Conduit
bodies shall be supported in a rigid and secure manner.

IMHO, splicing within an LB, LL, LR, C, T, etc. is not a respected trade practice, and not often seen.