#201369 - 05/29/11 08:03 PM LB Fittings
MJ2000 Offline
Member
Registered: 06/29/05
Posts: 17
Loc: Toronto, ON
Hi,
Is it allowed to make joints in LB fittings?

MJ
Top
Tools for Electricians:
#201372 - 05/29/11 08:25 PM Re: LB Fittings [Re: MJ2000]
dougwells Offline


Member
Registered: 05/03/03
Posts: 1137
Loc: kamloops BC Canada
I could be wrong,but I think as long as it meets the cu in box fill requirement It may be allowed.I would never splice service conductors though.
between meter and service disconnect that is. smile
Top
#201374 - 05/29/11 08:40 PM Re: LB Fittings [Re: MJ2000]
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
I think it is something to be avoided. There is no provision for bonding in an LB, it is difficult to maintain 150mm of conductors for splicing, and some may consider an LB to be a raceway, and we know joints are not permitted within raceways.That being said I dont think there is a rule that specifically prohibits splicing in an LB.
Top
#201414 - 05/31/11 04:24 PM Re: LB Fittings [Re: MJ2000]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
If the conduit body has a cubic inch area marked on it then you can splice in it according to 12-3034
Top
#201443 - 06/01/11 09:22 AM Re: LB Fittings [Re: mikesh]
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
My reading of 12-3034 is that it refers to boxes, whereas an LB would be considered a fitting - so should 12-3034 apply?
Top
#201449 - 06/01/11 04:26 PM Re: LB Fittings [Re: MJ2000]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Just a little insight from the NEC Standpoint:

314.16 (c) 2011 NEC

(2) With Splices, Taps, or Devices. Only those conduit
bodies that are durably and legibly marked by the manufacturer
with their volume shall be permitted to contain
splices, taps, or devices. The maximum number of conductors
shall be calculated in accordance with 314.16(B). Conduit
bodies shall be supported in a rigid and secure manner.

IMHO, splicing within an LB, LL, LR, C, T, etc. is not a respected trade practice, and not often seen.

_________________________
John
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 59 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals