The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by twh
Today at 06:28 AM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
2 registered (jraef, LongRunner), 188 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#201258 - 05/23/11 04:05 AM Are US breakers typically thermal-magnetic?
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2343
Loc: Vienna, Austria
Over on the German board the question arose, whether US breakers for residential use are typically equipped with both a thermal and an electromagnetic tripping device or only either of them.

In all countries that use DIN rail equipment they seem to alyways have both, is that true for the US too?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#201259 - 05/23/11 05:47 AM Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
The statement is true for breakers found in the typical panel.

There are some breakers used in motor control centers that lack the magnetic function.

Top
#201265 - 05/23/11 11:37 AM Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger]
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2343
Loc: Vienna, Austria
Thanks a lot! For motor controls, omitting the magnetic trip makes sense since the short-circuit protection can be achieved by a much larger fuse upstream.

Top
#201325 - 05/28/11 02:32 AM Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
Originally Posted By: Texas_Ranger
Over on the German board the question arose, whether US breakers for residential use are typically equipped with both a thermal and an electromagnetic tripping device or only either of them.

In all countries that use DIN rail equipment they seem to alyways have both, is that true for the US too?


It the same in France we have both thermal and magatic breakers as well but few of the breakers may not have magatic at all I know I have ran into hydrallic breaker { kinda oddball item }

Merci.
Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#201326 - 05/28/11 04:36 AM Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger]
Texas_Ranger Offline
Member

Registered: 12/17/01
Posts: 2343
Loc: Vienna, Austria
The hydraulic surely wasn't the typical 10, 16 or 20A household type, was it?

I'm interested in what you'd typically find in an apartment or single family home, as that was what the original discussion was concerned with.

Top
#201338 - 05/28/11 07:17 PM Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Reno,


Are we talking about FPE breakers? smile

Top
#201342 - 05/28/11 07:27 PM Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
This is a SqD QO GFCI I cut open to see what was inside.I was really interested in the GFCI part but you can see the breaker part too. It looks like it is thermal only.

_________________________
Greg Fretwell

Top
#201343 - 05/28/11 07:29 PM Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Harold, I cannot even attempt to explain the engineering miracle represented by FPE and their breakers.

Imagine ... a breaker that works so well in Canada that it's sold by Schneider Electric (alongside their competing Square D line), yet somehow fails to perform 'south of the border.'

Perhaps us hapless Yanks are simply not sophisticated enough to use these advanced devices laugh

Top
#201348 - 05/28/11 07:53 PM Re: Are US breakers typically thermal-magnetic? [Re: Texas_Ranger]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Reno,

I believe the FPE breakers actually worked well with a thermal overload. It was those quick short circuit faults that they didn't seem to see.

Top
#201410 - 05/31/11 09:48 AM Re: Are US breakers typically thermal-magnetic? [Re: renosteinke]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
Originally Posted By: renosteinke
There are some breakers used in motor control centers that lack the magnetic function.


Nope.

The "typical" breaker in a motor control center is Magnetic only. The thermal function is handled by the motor starter's overload relay.

Top