#201144 - 05/15/11 11:44 PM Continuous or not?
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
We all know that article 300.14 requires a minimum 6" of free conductor into each box. Is that continuous 6"?

what if it is 3" and one splices another 3". Is that code compliant?
_________________________
Be kind to your neighbor, he knows where you live

Top
2017 / 2014 NEC & Related Books and Study Guides
#201148 - 05/16/11 12:25 AM Re: Continuous or not? [Re: Niko]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I always read "free conductor" as meaning an unspliced conductor
_________________________
Greg Fretwell
Top
#201152 - 05/16/11 07:54 AM Re: Continuous or not? [Re: Niko]
sabrown Offline
Member
Registered: 12/12/02
Posts: 302
Loc: Ogden, Utah, USA
Someone could always misunderstand and think it is not required to be continuous. Given that argument I would then write them up on workmanship.

I believe that most if not all of us (even the engineers and maintanance people) have all had to try and deal with the miraculous "how did they even make the original connections?" receptacle replacement.
Top
#201154 - 05/16/11 08:22 AM Re: Continuous or not? [Re: gfretwell]
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
Originally Posted By gfretwell
I always read "free conductor" as meaning an unspliced conductor


Then at the time of final if you measure and they are short by 1" is the whole job red tagged or you would allow an extension?

I am not trying to argue with you. I want to see how this gets interpreted.

Personally i always use my stripper as a measuring tool and i measure from the face of the box.
_________________________
Be kind to your neighbor, he knows where you live

Top
#201156 - 05/16/11 10:53 AM Re: Continuous or not? [Re: Niko]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I might not be too hard to get along with if it was just one or two and close to 6" but if the guy made them all 3 or 4" he would be fixing it and splicing an extra wire on would not be acceptable. I have never had it come up. Usually this is seen on the rough and I saw the wires being longer most of the time.
If they did come up with a short one they managed to trick me wink
Maybe John, George or Harold will have a better answer for you.
_________________________
Greg Fretwell
Top
#201159 - 05/16/11 12:00 PM Re: Continuous or not? [Re: Niko]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
I have to agree with Gregs response. I check it on rough, and occasionally on final.

Where this arises as a situation.....is on the 'as-built' jobs that show up thru the CCO inspections. The 'as-built' basement conversions that the homeowner supposedly did. Procedure included the power be safed off, & the devices pulled to check the wiring. Then it's a red tag & a strong suggestion to contact a licensed electrical contractor to achieve code compliance. It's a real PITA.

Usually, free conductor length is not an issue with the 'sparkies', but we are all human.
_________________________
John
Top
#201199 - 05/18/11 01:25 AM Re: Continuous or not? [Re: Niko]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
As a foreman I sometimes encountered idiot apprentices who thought that our rough pulls existed so that they could earn trim scrap.

They ended up getting canned.

Short wires = more expensive work.

Yes, I've even had to re-pull conductors. ( rare )

Short taps = fumbling trim-out -- especially if apprentices.

If short taps occurred during wire pulls/ cable runs corrections were made promptly.

More generally, I never permitted any rough-in or separation to push the envelope of the NEC. Too expensive -- a route to poverty.

ONE example out of many: built up a 5,000kVA transformer room in the rough. Primary at 21.6kV Secondaries at 480Y277 and 208Y120.

Just imagine how many feeders ( 6" on primaries on down to 1.25" and 1" !! ) I allowed for an extra 1" clearance on stubs under the massive panel boards/ distribution sections.

Later, found out that the office had given us numbers in error! They were off by 1" ! I'd made it, though. My design margin had saved 850 man-hours. ( Ripping up the work encased in concrete 4 feet deep to move the pipes back into the room. )

Similar attitudes have saved my bacon WRT transformers, panel boards, the works.

If you are down to shaving inches off at j-boxes -- you are far gone. That's NOT where you make it. ( You can break it there, though. )


Edited by Tesla (05/18/11 01:34 AM)
_________________________
Tesla
Top
#201206 - 05/18/11 03:20 PM Re: Continuous or not? [Re: Niko]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Same rule in Canada and code is from the entry to the box to the cut off point. Homeowners are the worst for shorting splice wire and I have definitely had a few homeowners rewire a large area for cutting the Free conductor. By practice I grab the spliced wires and if the wire nuts are beyond my closed hand it passes. Short of that I get out my tape and check.
Top
#201208 - 05/18/11 06:57 PM Re: Continuous or not? [Re: Niko]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
I'd like to add my thoughts and experience. If you have a box where you have maybe three NM cables 14/2 w G, you will have 9 conductors that need to be long enough to extend outside the box three inches if the opening to the box is less than 8 inches in any direction. It is common practice to only have one of the G. wires left long to terminate on a device and the other 2 g. wires are spliced along with the long G. wire with a "Buchanan" or a wire nut.

I once had an inspection where the electrician was remodeling a basement that had been wired by a previous homeowner and the electrician cut out an old box and saved it for me. It had 2- 12/3 romex cables and an receptacle in a 1" deep box. I used it for a while in my code classes as this is what "NOT" to do. I don't know how he even was able to do it.

As for splicing a too short wire in a box- I can not find a code reference that would prohibit it albeit a bad practice. It's either splice it or relocate the box or pull new wire. I must be getting whimpy in my old age.
_________________________
George Little
Top
#201209 - 05/18/11 07:20 PM Re: Continuous or not? [Re: Niko]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
Ground wires are conductors, too. Those of use who do remodels appreciate a little length on all the ground wires.
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 80 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals