The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm≤ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 192 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#201104 - 05/11/11 10:36 AM Current waveform
will_87 Offline
New Member

Registered: 03/09/11
Posts: 5
Loc: england
My question is this:

After finally pinning down the boss Iíve eventually convinced him we can have our equipment replaced!

We had a data logger record our equipment for one week (voltage, currents, KW, KVAr, KVA ect) and decided to use the data to compile a report to indicate the size required for install.

The question is about the current waveform results:
Do we use the maximum average RMS value (the true effective value of the waveform) or the maximum max recorded value (the amplitude) to size are equipment.

I am as you can appreciate concerned about under sizing equipment due to fault or effectively over sizing and costing the company unnecessarily

Many, many thanks in advance for your thoughts and suggestion on this!

Top
#201107 - 05/11/11 06:26 PM Re: Current waveform [Re: will_87]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
All industry calcs are performed on RMS power.

True peak voltages are of concern only when designing circuits such as a low pass filter.
_________________________
Tesla

Top
#201110 - 05/12/11 03:08 AM Re: Current waveform [Re: will_87]
will_87 Offline
New Member

Registered: 03/09/11
Posts: 5
Loc: england
Many thanks for the reply Tesla,

What if the equipment in question were an at L.V 415V system?

Would this still be the peak current and not the peak to peak current?

Top
#201113 - 05/12/11 10:13 AM Re: Current waveform [Re: will_87]
sabrown Offline
Member

Registered: 12/12/02
Posts: 297
Loc: Ogden, Utah, USA
One weeks worth of data does not help much, but that depends on the type of equipment you are looking at. Our replies would be better if we knew what type of equipment you are looking ate. If you are looking at feeders and load centers your data would be better collected over a 6 month to one year period unless you have some way of ensuring worst case loading.

But yes still RMS current not peak to peak.

Shane

Top
#201223 - 05/20/11 06:45 AM Re: Current waveform [Re: sabrown]
RSmike Offline
Member

Registered: 11/27/02
Posts: 130
Loc: Holland, MI USA
I would be concerned if the peak current is waaaaay above the RMS. I'd want to know the duration of the 'peaks'.

You need to be able to supply RMS as well as the peak or you are going to starting popping fuses.

I do feel your pain. In work in a large mfg facility and it's always difficult to determine how much room is left on a bussbar without doing some data logging, field observations, and then some estimation (I hate to use the words 'best guess'). In the end that's what fuses are for.

But like sabrown sez...and unless I missed it in the thread...you'd need to tell us more about the load.

Top
#201228 - 05/20/11 07:35 PM Re: Current waveform [Re: will_87]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
Harmonic AC waveforms dictate that Peak Voltage = 1.414 x RMS.

Unless you've introduced non-harmonic back-EMF that's your answer.
_________________________
Tesla

Top