#200974 - 04/30/11 12:09 AM setting up a data logger
jackolsen Offline
Member
Registered: 02/11/08
Posts: 21
Loc: british columbia canada
I have an aemc simple logger 11 model l562.My question is on how to set this logger as to which scale multiplier setting to use.
input one is 0-1v scale choices are 10mv/ma,1mv/ma,100mv/a
1mv/a or 0.33mv/a this input is for a clamp amp probe

input two is 0-600vac the scale multiplier settings are 1,100 or 10
the manual that came with this unit does not give much info on setting up the scales multipliers.
I can make this unit work but would like a better understanding on how best set this logger up.
I use it to find problems in homes and business eg when did the voltage drop out or current rise etc.
can anyone recondmend a book on this topic?
Top
Tools for Electricians:
#200982 - 04/30/11 10:21 AM Re: setting up a data logger [Re: jackolsen]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
I would use the 600v scale set up 1:1 for 120/240.

You can also hook up the clamp to track line in current so you can see if the dip was caused by your load spiking or was a utility problem.
_________________________
Greg Fretwell
Top
#200995 - 05/02/11 01:37 AM Re: setting up a data logger [Re: jackolsen]
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
This Device _APPEARS AS_ a Power Monitor, for logging a Single Phase Circuit over a given Time Period.

Input #1 would be the Current Probe Input, via a Clamp-On type Ammeter (Current Transformer type Current Probe).
Connect a compatible CT to the "CH-1" Input on the Meter.
Set the Parameters for CH-1, per the specifications of the Current Probe used.
Clamp the CT around ONE Conductor on the Circuit to be Monitored.

Input #2 would be the Voltage Probe Input.
This may be via:
1: Voltage Probe Leads of the Current Probe,
or
2: a Pair of Alligator Clipped Voltage Leads, connected to the Two Wires of the Monitored Circuit, at a Termination Point (so as to measure the Circuit's Voltage).

The Multiplier settings for CH-2 _MIGHT BE_ as follows:

A: Using the Current/Voltage Probe: 100:1,
B: Using Alligator Clip Leads: 1:1

These figures are not device specific, so best to verify prior to actual use.

Do a Google Search for your Model Number. This might yield more information than what is found in the Document you have now.

Good luck... sorry I could not give you actual answers! frown

--Scott
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 124 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals