ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 17
Recent Posts
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
Dining room plugs
by watersparkfalls. 03/21/17 10:31 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,476 Are you busy
166,184 Re: Forum
160,637 Need opinion
Who's Online Now
0 registered members (), 54 guests, and 13 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#200941 - 04/28/11 10:04 PM Defective Panels  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,799
Brick, NJ USA
As the solar install titled "Bigger" is commisioned and fully operational, I came upon this point of interest.

Out of the 17,000+ total panels installed for the 4.26MW total system capacity there were only 18 rejected panels.

Sure sounds like kudos are in order for the "Made in USA" panels on this job.

The rejection reasons are 'output below spec'.



John

Green Building & Alternative Energy Related:

#200944 - 04/29/11 12:34 AM Re: Defective Panels [Re: HotLine1]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,313
Alaska
How did they test the panels? Were they passed through a test station in a controlled environment?


"Live Awesome!" - Kevin Carosa

#200949 - 04/29/11 06:10 AM Re: Defective Panels [Re: HotLine1]  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
AK.,

I think they spotted by thru the sub colleter control panels which they will check the current drawage from each section so if the X number of amps is lower than other they will check it closer to make sure which panel is bad and they will find it.

Merci,
Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#200950 - 04/29/11 09:25 AM Re: Defective Panels [Re: HotLine1]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,799
Brick, NJ USA
SparykinAk:
Marc hit the nail basically. The panels were tested at the mfg after assembly as you mentioned. During field testing, the 18 that were 'rejected' were discovered. IMHO, that is a small percentage.

The voltage output from the 18 was 'under performance spec'.

I am curious if anyone has any comments on other install fail/defect panels.


John

#200954 - 04/29/11 01:44 PM Re: Defective Panels [Re: HotLine1]  
Vindiceptor  Offline
Member
Joined: Mar 2011
Posts: 98
San Diego

What manufacturer and model if I may ask?

We have installed about 40k Yingli 230 modules in the past 18 months and as stated previously each combiner box is checked and each string's output (Isc and Vmp) are checked and so far all have had a voltage tolerance below 2% and a current tolerance below 3%, well below the rebate threshold.

The biggest issue we've had to date is the care and handling of the modules before, during and after their installation before turning the projects over to the owner, accidents happen and modules aren't cheap.


#200958 - 04/29/11 04:11 PM Re: Defective Panels [Re: Vindiceptor]  
Vindiceptor  Offline
Member
Joined: Mar 2011
Posts: 98
San Diego

Nevermind, I found the project online.

It's nice to see an American company producing modules in that volume AND that owners are willing to pay the higher price for them, that is hard to find.


#200963 - 04/29/11 08:23 PM Re: Defective Panels [Re: HotLine1]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,799
Brick, NJ USA


You may find some info on this project here at this link:

http://www.facebook.com/solarnation



John

#200964 - 04/29/11 08:24 PM Re: Defective Panels [Re: HotLine1]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,799
Brick, NJ USA
Manufacturer is 'Sun Solar'


John

#200973 - 04/30/11 02:52 AM Re: Defective Panels [Re: frenchelectrican]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,313
Alaska
That's how I do it by comparing with others of a string. There's are several manufacturers who are or were churning out panels a few years ago, Europe was buying up everything they could from the US that was not nailed down


"Live Awesome!" - Kevin Carosa

#200999 - 05/02/11 10:38 AM Re: Defective Panels [Re: HotLine1]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
John,


Did the manufacture take the defective panels back? If not, how did they get rid of the defective panels.


Page 1 of 2 1 2

Member Spotlight
Niko
Niko
Campbell, CA
Posts: 356
Joined: August 2006
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.029s Queries: 16 (0.005s) Memory: 0.8161 MB (Peak: 0.9990 MB) Zlib enabled. Server Time: 2017-03-26 07:21:07 UTC