The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
Yesterday at 09:33 AM
breaker meltdown
by crselectric
Yesterday at 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 17
gfretwell 9
sparky 9
sparky66wv 8
Vlado 6
Who's Online
1 registered (geoff in UK), 231 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#200852 - 04/22/11 09:38 AM O/T pole pigs with 240/480 secondaries
LarryC Offline
Member

Registered: 07/05/04
Posts: 775
Loc: Winchester, NH, US
I was looking at the classified ads on this site. Somebody has a bunch of pole transformers that have 240/480 secondaries.

In what application would they be used?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#200867 - 04/23/11 05:05 PM Re: O/T pole pigs with 240/480 secondaries [Re: LarryC]
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I see these around mine sites quite a bit. Many mine sites use 240 or 480 3 phase Delta ungrounded systems as permitted by 250.21 (A)(4). These transformers could also be used for a corner grounded Delta.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#200872 - 04/23/11 06:45 PM Re: O/T pole pigs with 240/480 secondaries [Re: Tom]
LarryC Offline
Member

Registered: 07/05/04
Posts: 775
Loc: Winchester, NH, US
OK, thanks.

Top
#200880 - 04/24/11 06:25 PM Re: O/T pole pigs with 240/480 secondaries [Re: Tom]
LarryC Offline
Member

Registered: 07/05/04
Posts: 775
Loc: Winchester, NH, US
Is 240/480 delta a common configuration for oil fields too?

Top
#200881 - 04/25/11 12:00 AM Re: O/T pole pigs with 240/480 secondaries [Re: LarryC]
Lostazhell Offline
Member

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
yes it is... 99% of the 480V running around the oil fields in western Kern Co, CA are ungrounded delta sec's. with delta primary on 12KV systems and Wye on 21KV systems

Top