The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
sparky 4
Who's Online
0 registered (), 265 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#200697 - 04/14/11 08:54 PM Service Disconnect
SJT Offline

Registered: 07/24/02
Posts: 242
A Service Main disconnect could be outside the building or in the Bldg. right?
If the main is outside (near a transformer)then the first panel it feeds in the Bldg. would be a sub panel?

2014 / 2011 NEC & Related Books and Study Guides
#200700 - 04/14/11 11:09 PM Re: Service Disconnect [Re: SJT]
gfretwell Offline


Registered: 07/20/04
Posts: 9023
Loc: Estero,Fl,usa
Technically the service disconnect just has to be on the property but your AHJ may still want a disconnect on/in the building.
Yes that will become a feeder and you need to run the ECG along with a ground. As long as that is the feeder for the whole building, you can use 210.15(B)(6) in a dwelling. (Not commercial)

Edited by gfretwell (04/15/11 01:04 AM)
Edit Reason: Make the correction Niko pointed out
Greg Fretwell

#200701 - 04/15/11 12:36 AM Re: Service Disconnect [Re: SJT]
Niko Offline

Registered: 08/17/06
Posts: 358
Loc: Campbell, CA
Greg meant, 310.15(B)(6) for 2008 and 310.15(B)(7) for 2011
Be kind to your neighbor, he knows where you live

#200703 - 04/15/11 01:06 AM Re: Service Disconnect [Re: SJT]
gfretwell Offline


Registered: 07/20/04
Posts: 9023
Loc: Estero,Fl,usa
Thanks. I guess I should turn up the light when I type

I am not on the 2011, in protest of the CD thing wink
Greg Fretwell

#200714 - 04/15/11 09:00 PM Re: Service Disconnect [Re: SJT]
HotLine1 Offline


Registered: 04/03/02
Posts: 6791
Loc: Brick, NJ USA
Be cautious on the location 'within the building'. Unprotected, unfused, conductors within a building, the distance allowed is not specific in the NEC. For the most part, it's left up to the local AHJ. I hear 12", 5', 3'4", but there is NO distance within the book & never was.

A main inside is accepted 'nearest to the point of entry', unless we use the 2" of concrete/brick exception. It all boils down to the AHJ's 'nearest' definition