#200651 - 04/12/11 12:35 PM Feeder size
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
I seem to remember something in the code that talked about the minimum size feeder conductor. I know the feeder conductor must be capable of carrying the connected load and that's not what I referencing. I seem to remember that the minimum size feeder being size #10 AWG. Please tell me I'm right or wrong.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#200654 - 04/12/11 03:00 PM Re: Feeder size [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I can't say you are wrong but I don't know where that might be. I looked again in 215 and 310, I don't see it.
_________________________
Greg Fretwell
Top
#200656 - 04/12/11 05:28 PM Re: Feeder size [Re: George Little]
Niko Offline
Member
Registered: 08/17/06
Posts: 356
Loc: Campbell, CA
Are you talking about outside feeder overhead span?
225.6(A)(1) Minimum size of 10AWG
_________________________
Be kind to your neighbor, he knows where you live

Top
#200657 - 04/12/11 06:32 PM Re: Feeder size [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Nice catch wink
_________________________
Greg Fretwell
Top
#200659 - 04/12/11 07:02 PM Re: Feeder size [Re: George Little]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Something regarding the grounded conductor (feeder) being #10 minimum?

_________________________
John
Top
#200665 - 04/13/11 09:04 AM Re: Feeder size [Re: George Little]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Thanks guys, I guess you came up with the same things I did. I guess it must have been one of my "vest pocket rules" ha ha ha
_________________________
George Little
Top
#200668 - 04/13/11 10:26 AM Re: Feeder size [Re: George Little]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You have to scratch your head to come up with a scenario where a feeder would be less than 30a but I suppose it can happen. A possibility would be a feeder to a shed that terminates in a 2 pole <20a breaker> disconnect in the shed, serving as the disconnect and also supplemental overcurrent protection. Technically any conductor on the load side of the service disconnect and on the line side of an overcurrent device is a feeder.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 40 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals