#200609 - 04/10/11 08:24 AM Drop Ceiling Lighting
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
The question is: MUST you use troffers ("lay in fixtures") to provide light through a suspended ceiling?

I recently saw a home with a finished basement. A suspended ceiling was installed. for lighting, ordinary strip fixtures were installed to the 'hard' ceiling above, and lens panels were put in the grid underneath the fixtures.

(I always wondered why I always had to trim the home-center lenses a bit!)

Details of this specific installation aside, it made me wonder if there was anything wrong with the very concept.
Top
2017 / 2014 NEC & Related Books and Study Guides
#200611 - 04/10/11 11:01 AM Re: Drop Ceiling Lighting [Re: renosteinke]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 897
Loc: Chicago Illinois USA
Every home that I've seen has been done with striplights and a plastic panel below. It's pretty easy to see the unevenness of the light from above...I wonder if that's because the manufactured troffers do a better job of spreading out the light before it hits the lens.
_________________________
Ghost307
Top
#200612 - 04/10/11 11:04 AM Re: Drop Ceiling Lighting [Re: renosteinke]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Not sure I'd do it in my home. I don't see it as a code issue unless they were cord and cap connected. I have seen "cost conscious" versions of this that also include a reflector that almost fits the 2x4 space in a standard drop ceiling grid.


Edited by George Little (04/10/11 11:05 AM)
Edit Reason: typo
_________________________
George Little
Top
#200614 - 04/10/11 11:47 AM Re: Drop Ceiling Lighting [Re: renosteinke]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
I have to agree with George. You may find a 110.3 IF there is any indication from the fixture (luminaire) mfg that the fixture is designed for surface mounting.

That may be considered 'pushing the envelope' but....ya never know.
_________________________
John
Top
#200615 - 04/10/11 11:50 AM Re: Drop Ceiling Lighting [Re: renosteinke]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I did this on an addition in my old house in Md (late 70s) and I would not do it again. I learned a lot of lessons on that project wink

The reason you have to trim the panels is they are actually 2x4 and the grid is 2x4 on center. You are trimming off the thickness of the T bar. YMMV it seems, some seem to be a tad smaller than 2x4 and go in without trimming.
_________________________
Greg Fretwell
Top
#200619 - 04/10/11 12:02 PM Re: Drop Ceiling Lighting [Re: renosteinke]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Greg:

I think Reno was refering to using 'big box' lenses as replacements for 2x4 troffers. Basically, something that I can say 'been there, done that'!

Yes, I also had channel strips, with 'custom cut' lenses in our old house. And, I will not do that again.



_________________________
John
Top
#200623 - 04/10/11 02:39 PM Re: Drop Ceiling Lighting [Re: renosteinke]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
Iíve seen that type of install a lot over the years, especially in older 1970ís kitchens and basements. I'm wondering if the manufacture states surface mounting only as mentioned, since the manufacture most likely doesnít specify what particular surface is approved for mounting, I'm guessing that the suspended ceiling still wouldn't qualify as structural ceiling in this situation.
Top
#200628 - 04/10/11 06:40 PM Re: Drop Ceiling Lighting [Re: renosteinke]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I am just talking about screwing a strip on the structural ceiling above the center of a 2x4 T bar hole and dropping a diamond molded lexan panel in there instead of a ceiling panel.
_________________________
Greg Fretwell
Top
#200630 - 04/10/11 07:25 PM Re: Drop Ceiling Lighting [Re: renosteinke]
schenimann Offline
Member
Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
I wired a tree house for a family and they wanted me to pick out a fixture that would be safe and fitting for their kids. I hate picking out fixtures for somebody else. I ended up put strip lights between the ceiling joists and framed in a slot for a panel to slide in below the joists. I ordered a panel with the clouded sky printed on it. It looked pretty cool in the tree house, like a hole in the ceiling.
Top
#200633 - 04/11/11 04:22 AM Re: Drop Ceiling Lighting [Re: renosteinke]
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Hey Schenimann- Did you get a permit, an inspection and a C of O? ha ha ha
_________________________
George Little
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 102 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 10/19/00
Posts: 2724

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals