#200571 - 04/07/11 08:45 PM PVC BETWEEN GALV PIPE
lite bulb Offline
Member
Registered: 02/12/06
Posts: 76
Loc: wilm,de.
I'm wiring a 480v motor from the starter I'm going down into the concrete floor with galv pipe to protect from damage, afraid pvc will get broken above the slab, then change to 70'pvc run in the slab then back to galv when I exit the slab to the motor. Does the code allow pvc pipe between galv
Top
2017 / 2014 NEC & Related Books and Study Guides
#200572 - 04/07/11 09:18 PM Re: PVC BETWEEN GALV PIPE [Re: lite bulb]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Just be sure you bond the exposed sections of galvanized and run a hard wire EGC.
_________________________
Greg Fretwell
Top
#200576 - 04/08/11 05:13 AM Re: PVC BETWEEN GALV PIPE [Re: lite bulb]
lite bulb Offline
Member
Registered: 02/12/06
Posts: 76
Loc: wilm,de.
I under stand the bonding of the exposed galv. and a grounding conductor in the pvc but what is a hard wire, is it a solid wire.
Top
#200577 - 04/08/11 05:49 AM Re: PVC BETWEEN GALV PIPE [Re: lite bulb]
ghost307 Offline
Member
Registered: 05/09/05
Posts: 900
Loc: Chicago Illinois USA
I think Greg is saying that since you can't use PVC conduit to serve as a ground return path (equipment grounding conductor), sometimes known to its dear and intinmate friends as a 'ground wire', you need to run a physical wire through the conduit run to serve that purpose.
_________________________
Ghost307
Top
#200578 - 04/08/11 05:56 AM Re: PVC BETWEEN GALV PIPE [Re: lite bulb]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Yup, sorry, that must be an old timey or a regional term. I was referring to an equipment grounding conductor. Actually if it is bigger than #10 it can't be solid.
_________________________
Greg Fretwell
Top
#200587 - 04/08/11 05:05 PM Re: PVC BETWEEN GALV PIPE [Re: gfretwell]
lite bulb Offline
Member
Registered: 02/12/06
Posts: 76
Loc: wilm,de.
Thanks for the help guys.
Top
#200652 - 04/12/11 02:44 PM Re: PVC BETWEEN GALV PIPE [Re: lite bulb]
Tesla Offline
Member
Registered: 06/16/04
Posts: 1273
Loc: Sacramento, CA
Excuse me, but liquid wire will just slump down into the PVC.

It's going to have to be solid wire.

I prefer stranded.
_________________________
Tesla
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 40 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals