The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 262 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#200459 - 04/01/11 10:56 PM Dropping 1 leg of 480 to control site lighting
wewire2 Offline
Member

Registered: 11/14/02
Posts: 246
Loc: California
Is there a code reference that prohibits dropping 1 leg of a 480 circuit to control HID lighting? I notice 410.141(B) only applies to fixtures exceeding 1000V.

Top
2014 / 2011 NEC & Related Books and Study Guides
#200480 - 04/02/11 07:37 PM Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Wewire2:

Care to explain the above with a little more clarity please.
_________________________
John

Top
#200485 - 04/02/11 08:39 PM Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2]
wewire2 Offline
Member

Registered: 11/14/02
Posts: 246
Loc: California
Sure, thanks John.
3 phase 480, 3 wire is pulled to a light pole with 4
fixtures on the pole. The site engineer wants to drop legs to control the lights separately. I don't like the design but can't seem to find anything that prohibits it as long as the required disconnecting means is in place. What do you think?

Top
#200486 - 04/02/11 10:05 PM Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Look at 410.104(B). I don't know if it applies but it could. Not sure what the Design Professional has in mind but this might help.


Edited by George Little (04/02/11 10:06 PM)
_________________________
George Little

Top
#200488 - 04/02/11 11:10 PM Re: Dropping 1 leg of 480 to control site lighting [Re: wewire2]
wewire2 Offline
Member

Registered: 11/14/02
Posts: 246
Loc: California
George, I think that's what I'm looking for. The "auxiliary
equipment" terminology threw me off and I skimmed right past it. It appears that the term auxiliary equipment refers to ballast. Thank you sir!

410.104(B)Where supplied by ungrounded conductors of a circuit, the switching device of auxiliary equipment shall simultaneously disconnect all conductors.

Top