#200399 - 03/30/11 05:33 PM Splice in service disconnect
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
A 400amp main disconnect will need to be added outside a Building. Existing is a 400 amp main circuit breaker panel in the utility room. The Arc flash rating turned out to be a Cat. 4 for the Panel.(you have to wear a space suit) so by installing a Disconnect between the Panel and the transformer, the engineer says it will go to a category 2. This is fed from a pad mount transformer with the metering mounted on the outside. Can the feeders from the transformer be spliced in the disconnect if not long enough, to go to the line side of the switch? Or will we have to install a 2'x2' junction box. Existing, is the 4" LB going to the back of the Main Panel.
Sorry about the long story - Thanks, SJT
Top
Work Gear for Electricians and the Trades
#200401 - 03/30/11 07:29 PM Re: Splice in service disconnect [Re: SJT]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
IMHO, run this past the local AHJ first. Also you may have to run it by the local POCO. 'Line' side may be POCO jurisdiction. Using barrel crimps should be acceptable.

_________________________
John
Top
#200432 - 04/01/11 07:06 AM Re: Splice in service disconnect [Re: SJT]
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
I'm sorry I only have my 2008 NEC with me, ( we are still on that code) but would 230.33 be of use in this case?
Top
#200437 - 04/01/11 08:03 AM Re: Splice in service disconnect [Re: SJT]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
harold:
230.33 refers you to 110.14 regarding splicing methodology, and refers to 300.xx articles which I understand are not applicable in the OP.

I mentioned the local POCO, and AHJ for a few reasons. Here (PS) crimp splices are acceptable on a case by case basis, as they are by me, and most other AHJs. Extending an existing lateral feeder to terminate at the line side of a disconnect switch, in lieu of replacement of that feeder can be acceptable. Crimp splice; feeder in acceptable condition, and sufficient 'space' within the disco.

_________________________
John
Top
#200464 - 04/02/11 10:19 AM Re: Splice in service disconnect [Re: SJT]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I only had the "splice in the disco" come up once and I agreed to the irreversible crimp splice, simply because any alternative was very burdensome on the installer and I did not see any particular hazard. We were literally talking about a foot of wire.
_________________________
Greg Fretwell
Top
#200468 - 04/02/11 10:33 AM Re: Splice in service disconnect [Re: SJT]
SJT Offline
Member
Registered: 07/24/02
Posts: 241
Loc: PATCHOGUE, N.Y.
Thanks for the inputs,
I think I'll go with the barrel crimps, if the wires are not long enough.
SJT
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 30 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals