#200089 - 03/20/11 07:51 PM What type of wire?  
schenimann  Offline
Member
Joined: Feb 2008
Posts: 193
Western North Carolina
I did a small panel change on Friday. Existing were fuses with a 60amp main. They didn't want to do service upgrade, only get rid of the fuses. They did want to however install a 125amp panel for future possible upgrades. The se is "anaconda" #2 copper. What wire type is this? What do they coat the strands with to give them the gray coating on the outside?


Work Gear for Electricians and the Trades

#200097 - 03/20/11 11:58 PM Re: What type of wire? [Re: schenimann]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
I don't have any specific info on Anaconda SE cable, but tin, silver or nickel are commonly used to coat annealed copper wire like that.


#200098 - 03/21/11 12:12 AM Re: What type of wire? [Re: schenimann]  
schenimann  Offline
Member
Joined: Feb 2008
Posts: 193
Western North Carolina
the coating did have 75deg on the coating. Is it considerid copper and can I use that column of 310.16 in the copper ampacity chart for it? Just trying to make sure I put the proper size breaker in. The panel had a 60amp breaker, but if I could put in a 100amp main in that would save them a service upgrade. It was acutally #3, not #2.


#200100 - 03/21/11 01:22 AM Re: What type of wire? [Re: schenimann]  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
I will take this a grain of salt due I do not have the NEC chart with me at the moment but IIRC the smallest unground conductor you can use for 100 amp service is #4 or 25mm one of the two but becarefull some inspectors may reject that and have to use #2 or 35mm conductors size so that kinda of fineline to walk on this one.

Merci.
Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#200153 - 03/22/11 10:38 AM Re: What type of wire? [Re: schenimann]  
Texas_Ranger  Offline
Member
Joined: Dec 2001
Posts: 2,392
Vienna, Austria
No matter whether it's tinned or not, it's considered copper. The only alternative is aluminum, but that should be obvious enough if you cut the wire and look at the cut. Aluminum is silver all the way through.


#200155 - 03/22/11 02:27 PM Re: What type of wire? [Re: schenimann]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,798
Brick, NJ USA
By table 310.15, #3 Cu SE is good for 110 amps, so a 100 amp cb would be compliant.



John

#200164 - 03/23/11 12:39 AM Re: What type of wire? [Re: HotLine1]  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
Originally Posted by HotLine1
By table 310.15, #3 Cu SE is good for 110 amps, so a 100 amp cb would be compliant.



Is this type of SE cable is rated at 60C rating or on 75C rating I know this is for service entrance but if used for feeder then the bet is off it have to stay with 60C rating.

Merci,
Marc

Last edited by frenchelectrican; 03/23/11 12:40 AM.

Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#200170 - 03/23/11 09:48 AM Re: What type of wire? [Re: schenimann]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,798
Brick, NJ USA
Marc:
You are quite correct. The OP eluded to it being service cable from his description.



John

#200175 - 03/23/11 05:09 PM Re: What type of wire? [Re: schenimann]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,057
Estero,Fl,usa
If you are using the 310.15(B)(6) table, temperature does not come into it. There may be a question about if it applies but he was talking about the "main" so I assume it does.
That could be the service entrance or the "main power feeder" between the service disconnect and the main distribution panel. He did say "SE" not "SER" so it sounds like the service entrance.


Greg Fretwell

#200184 - 03/24/11 12:04 AM Re: What type of wire? [Re: schenimann]  
schenimann  Offline
Member
Joined: Feb 2008
Posts: 193
Western North Carolina
It is the service entrance from the meter to the panel.


Page 1 of 2 1 2

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.023s Queries: 16 (0.004s) Memory: 0.8163 MB (Peak: 1.0012 MB) Zlib enabled. Server Time: 2017-03-24 10:17:13 UTC