#200089 - 03/20/11 04:51 PM What type of wire?
schenimann Offline
Member
Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
I did a small panel change on Friday. Existing were fuses with a 60amp main. They didn't want to do service upgrade, only get rid of the fuses. They did want to however install a 125amp panel for future possible upgrades. The se is "anaconda" #2 copper. What wire type is this? What do they coat the strands with to give them the gray coating on the outside?
Top
Work Gear for Electricians and the Trades
#200097 - 03/20/11 08:58 PM Re: What type of wire? [Re: schenimann]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
I don't have any specific info on Anaconda SE cable, but tin, silver or nickel are commonly used to coat annealed copper wire like that.
Top
#200098 - 03/20/11 09:12 PM Re: What type of wire? [Re: schenimann]
schenimann Offline
Member
Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
the coating did have 75deg on the coating. Is it considerid copper and can I use that column of 310.16 in the copper ampacity chart for it? Just trying to make sure I put the proper size breaker in. The panel had a 60amp breaker, but if I could put in a 100amp main in that would save them a service upgrade. It was acutally #3, not #2.
Top
#200100 - 03/20/11 10:22 PM Re: What type of wire? [Re: schenimann]
frenchelectrican Offline


Member
Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
I will take this a grain of salt due I do not have the NEC chart with me at the moment but IIRC the smallest unground conductor you can use for 100 amp service is #4 or 25mm one of the two but becarefull some inspectors may reject that and have to use #2 or 35mm conductors size so that kinda of fineline to walk on this one.

Merci.
Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#200153 - 03/22/11 07:38 AM Re: What type of wire? [Re: schenimann]
Texas_Ranger Offline
Member
Registered: 12/17/01
Posts: 2351
Loc: Vienna, Austria
No matter whether it's tinned or not, it's considered copper. The only alternative is aluminum, but that should be obvious enough if you cut the wire and look at the cut. Aluminum is silver all the way through.
Top
#200155 - 03/22/11 11:27 AM Re: What type of wire? [Re: schenimann]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
By table 310.15, #3 Cu SE is good for 110 amps, so a 100 amp cb would be compliant.

_________________________
John
Top
#200164 - 03/22/11 09:39 PM Re: What type of wire? [Re: HotLine1]
frenchelectrican Offline


Member
Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
Originally Posted By HotLine1
By table 310.15, #3 Cu SE is good for 110 amps, so a 100 amp cb would be compliant.



Is this type of SE cable is rated at 60C rating or on 75C rating I know this is for service entrance but if used for feeder then the bet is off it have to stay with 60C rating.

Merci,
Marc


Edited by frenchelectrican (03/22/11 09:40 PM)
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#200170 - 03/23/11 06:48 AM Re: What type of wire? [Re: schenimann]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6833
Loc: Brick, NJ USA
Marc:
You are quite correct. The OP eluded to it being service cable from his description.

_________________________
John
Top
#200175 - 03/23/11 02:09 PM Re: What type of wire? [Re: schenimann]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
If you are using the 310.15(B)(6) table, temperature does not come into it. There may be a question about if it applies but he was talking about the "main" so I assume it does.
That could be the service entrance or the "main power feeder" between the service disconnect and the main distribution panel. He did say "SE" not "SER" so it sounds like the service entrance.
_________________________
Greg Fretwell
Top
#200184 - 03/23/11 09:04 PM Re: What type of wire? [Re: schenimann]
schenimann Offline
Member
Registered: 02/18/08
Posts: 194
Loc: Western North Carolina
It is the service entrance from the meter to the panel.
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 117 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals